sharpy1983

Hi all,

Been testing on part of the motorway network and come across a few Ze readings which are a little higher than should be for a TNCS supply. Getting 0.45 Ohms from one supply and 0.51 from another.

Been told that the DNO will just state that 0.35Ohms is a guide and that they wont bother their arses to look into it? Is this really the case? Going to give the DNO a call in the morning and hopefully get them to raise a job so they can attend, was just wondering of anyone has had any similar experiences.

Also, If for example, the main cut-out is a BS1361 100Amp, but my Zs at the dist point is higher than the maximum Zs stated in BS7671, am I ok to replace the fuse for a lower rating or again, is this a DNO job?

Many Thanks
 
they should sort out the high Ze. your max Zs is dependent on the circuit ocpd, not the cut-out fuse, assuming the circuit is fused down,
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
High Ze and Zs at PDU.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
1

Thread Tags

Tags Tags
pdu

Advert

Thread statistics

Created
sharpy1983,
Last reply from
telectrix,
Replies
1
Views
1,003

Advert

Back
Top