Hi All just doing some testing in my friends house as he has just moved into a new home and wants some work done.

Whilst i was carrying out a ze test on the upstairs ring final circuit i found a spur which had a ze of 2.4 ohms seemed a bit high to me, i tried tightening the earth etc changing the socket as it was a cheap on still the same reading?

Anyone have any pointers or had this problem before?

Also whilst carry out a ze test i found that when reconecting the main earth i had a few small sparks emit from it. I left the main earth disconnected and testing on volts the main earth to the ground and had 55v

The supply is a tn-c-s system

Just wondered if any of you have come across this before?

Thanks in advance

- - - Updated - - -

Zs on ring final do apologise it is late!!!!!!
 
Also whilst carry out a ze test i found that when reconecting the main earth i had a few small sparks emit from it. I left the main earth disconnected and testing on volts the main earth to the ground and had 55v

I assume that the installation was isolated before you commenced with the Ze test?

That apart, how did you measure the Suppliers 'earth' to real earth? Since the suppliers earth is the neutral and 55v is way too high. The DNO allow something in the region of 11V max.
 
need to start at the beginning. Zefirst, then Zs. a high reading for Zs could be caused by 1. main switch/isolator. 2. RCD. 3 MCB. 4. poor connections.
 
Is it just high Zs on the one socket, if so check line and CPC connections at both ends i.e at the socket and at the point at which it connects to the ring ( if you can find it)
 
Hi guys

I had a zs reading of 2.4 ohms at the spured socket
had a ze reading of 0.16 ohms

Ze is fine as for a tncs max is 0.35 ohms.

Max zs on 32a breaker type b is 1.16 ohms
not sure why its so high.
All othe sockets on the ring seem ok and within the 1.16 ohms?
 
test at the back of the socket, on the terminals. could be a bit of resistance in the pin connections in the socket.
 
Just popped over there found that the socket feeding the spur is infact a spur itself.
I Think im going to add them both into the ring final Circuit will be easy too as all cables are in the loft dropping down stud walls.
couldnt get to the socket i think its fed from as there was loads of stuff in the way hate it when that happens!

Didnt get chance to test again will do some testing tommorrow.
 

Reply to High ze at spur? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top