High ze low zs anyone help please | on ElectriciansForums
Discuss High ze low zs anyone help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
P
pablo4321
been to job with another experienced electrician the system was a tt he did a ze test which was 182 ohms but when did the zs at the sockets the zs was 0.56 ohms i thought ze plus R1PLUS R2 SHOULD BE READING ARE THESE READINGS OK
Good one this.
More than likely they share a water pipie with a neighbout (it happens) thats metal all the way, and the neighbour is... Yep TNCS. Try disconnecting the main bond to the water supply & re test (safely if course). And /or other services.
Flummoxed me for a while that one (TT HOUSE, Ze 17.8, Zs at sockets 0.3)
pablo, in post 1 you said it was TT, then in post 3 you said PME with a rod. which is it? if it's TT, then the low Zs is due to parallel paths through bonding services.
Was the Ze done with the main earthing connection disconnected from the installation? This is the only way you can get an accurate result.
Cheers...........Howard
Reply to High ze low zs anyone help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!