Compleated a consumer unit change the other day and when testing the Ze I got a reading of 0.43, I know it should be 0.35 so what should i do?.

All the other readings was fine such as zs values, so should I compleate the certificate and make a note of the high Ze. Then phone the supplyer to investigate as it is down to them at the end of the day.

I checked all the connections and 0.43 was the best i could get.

Thanks.
 
you've answered your own question. it's the DNO you need to contact, not necessarily the supplier. they 2 are often different.
 
I had a 0.42 reading the other day, rang the DNO and they were out and "fixed" it within two hours before I had finished 1st fix. Admittedly they only tightened the neutral connection but I have found they are responsive to these requests.
If you have completed the install then really you cannot sign off the certificate as the install does not meet BS7671 so you need the DNO to sort it first.
 
Hi mcm, ensure your Ze reading is from a high current loop test (NOT No-Trip). If you are confident in your “high” reading, you should reconnect the main earthing conductor, replace any covers and ensure that the installation remains isolated and locked-off. Contact the DNO immediately; they will issue a priority call-out to the site because a potential PME fault may effect other installations in the area in addition to yours. In my area the DNO aim to respond within an hour of the call. You should not leave the site, as you will need to liaise with the DNO operative when he/she arrives. You should not complete the installation paper work at this point. The DNO operative will test your installation with their very high current EFLI tester if the reading is >0.35 ohms, he will carry out other tests/actions to find the fault and correct it. If on the other hand he finds EFLI is within the normal range < 0.35 ohms, you may be given either the measured value and the make; type; serial number of the instrument used or most operatives however will be less committal and just give you a maximum 0.35 ohms for the PME network. When the fault is corrected or you are told the installation is within the normal range, the DNO will give you permission to re-energise the installation, at which point you can continue testing. Record the value given and/or your new results on your installation paper work. I usually log the initial reading and my/DNO actions there after until permission to re-energise is given, as a contemporaneous note addendum to the report or certificate.
 
Last edited by a moderator:

Reply to the thread, titled "High Ze on tncs system" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
High Ze on tncs system
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
mcm,
Last reply from
Knobhead,
Replies
6
Views
6,016

Advert

Back
Top