Question for you. Was testing a flat, it’s a massive house that’s been split into flats. All meters are in cupboard at front of the house. 10mm twin and earth from the fuse for this flat goes into a big isolator, from that isolator a 2 core 16mm armour supplies this flat, who’s responsible for that armour? The DNO or me?
 
The thread is titled High Ze and the question is what is the problem.

From your description it is hard to envisage exactly what you have, how long is the 10mm² t&e run and how long is the swa run?
Anything after the suppliers metering belongs to you
 
The thread is titled High Ze and the question is what is the problem.

From your description it is hard to envisage exactly what you have, how long is the 10mm² t&e run and how long is the swa run?
Anything after the suppliers metering belongs to you
Sorry. Bit at the end didn’t post, was getting a Ze of 0.41 for a TNS system which I know is fine but still seems to be a high reading for a Ze, the 10mm T+e is about half a meter and the swa is roughly 10-15m hard to tell can’t really see what route they’ve taken
 
If you are concerned about the SWA you need the earth loop measurement both ends of it, so at the Isolator and at the consumer unit, and that will tell you if you have reason to be concerned or not.

Unless there was something else suggesting an issue I wouldn't generally be worrying about a TNS Ze of 0.41 ohms, you might be a good distance from substation after all.
 

Reply to High Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope you get better soon .sounds quite serious
    • Friendly
    • Like
Replies
12
Views
758
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
806
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top