just out of curiosity what the L1-L2 +E1+E2 reading?
What are they?!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss High ZS but R1+R2 and Ze ok in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
just out of curiosity what the L1-L2 +E1+E2 reading?
Will try this one. Thanks
What are they?!
what is the total restance of the complete Phase and CPC conductors on the ring?
The Zs should be approximatly 1/4 of it.
what is the total restance of the complete Phase and CPC conductors on the ring?
The Zs should be approximatly 1/4 of it.
The OP actually said that he's already done that in the first post, and reiterated that a few posts later, including cross connection of line and neutral too.
It sounds like he knows how to test a ring.
Yup done r1+r2 at all outlets. All within .05 of each other. Max was .64 ohms
Gonna check RCD for its resistance. Also could be my meter as others have had problems by the sounds of it with the Trip lock on the Easi Test.
By calc (Zs = Ze + (r1+ r2) the circuit passed. The max allowed Zs is 1.16 for the circuit and .94 is under this value.
This leads me to belive its the meter, the resistance of the RCD or my test leads.
Timo the 1.16 is that the tabulated value or the 80% corrected value? not got BRB to check.