And that's why type D aren't the best idea when type C is available.
Isn't a C type 0.87? I might be wrong I've just done it on my calculator rather that check the regs. But it would mean a C type wouldn't work for one of them results. Could always drop to a 16A type c maybe if they are 2.5mm's...that'll give you 1.09. D types are awful, avoid like the plague. All depends on the load you have on the circuit really, shame they didn't record it.
 
Other options for high zs would be rcbos tho may have problems with nuisance tripping or localised supplementary bonding of the lighting circuits
 
Isn't a C type 0.87? I might be wrong I've just done it on my calculator rather that check the regs. But it would mean a C type wouldn't work for one of them results. Could always drop to a 16A type c maybe if they are 2.5mm's...that'll give you 1.09. D types are awful, avoid like the plague. All depends on the load you have on the circuit really, shame they didn't record it.
Yes sorry your correct ,so one of the circuits would still be over
 
From past experience it has been the inrush start current that has been the problem on higher wattage low bay fittings so it may be interesting to know how many fittings being switched on at one time on each MCB.It will also be interesting to know Zdb and r1 +r2 and how much any parallel path of say structural steel is playing. Installing a RCBO may be the answer .
 

Reply to High zs on low bay lighting circuits in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top