robo83
Good morning,
I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.
R1+R2 measured 1.68ohm
Ze 0.18
Tncs
This puts the circuit over the permitted zs. I begun seeking out the issue.
However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'
Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?