High Zs on ring final circuit | on ElectriciansForums

Discuss High Zs on ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

robo83

-
Joined
May 23, 2016
Messages
180
Reaction score
48
Location
Birmingham
Good morning,

I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.

R1+R2 measured 1.68ohm
Ze 0.18
Tncs

This puts the circuit over the permitted zs. I begun seeking out the issue.

However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'

Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?



Sent from my SM-N910F using Tapatalk
 
Good morning,

I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.

R1+R2 measured 1.68ohm
Ze 0.18
Tncs

This puts the circuit over the permitted zs. I begun seeking out the issue.

However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'

Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?



Sent from my SM-N910F using Tapatalk


What was the Measured Zs and what OCPD are you using?
 
Good morning,

I was recently at a job and had a discussion with another Electrician regards a high Zs reading on a ring final circuit.

R1+R2 measured 1.68ohm
Ze 0.18
Tncs

This puts the circuit over the permitted zs. I begun seeking out the issue.

However the other electrican said although this was above the permitted zs it can be noted on the cert as 'zs doesn't not comply but rcd protection on the circuit so1667ohms permitted'

Can somebody enlighten me please. Ive sent this on TT Installs but wouldn't expect this to be allowed on a tncs?



Sent from my SM-N910F using Tapatalk

Without the Zs reading how on earth do you expect us to be able to offer a helpful comment?


Sent from my iPad using Tapatalk
 
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk
 
So there's surely an issue with your CPC (it should be around 0.5 ohms for 2.5/1.5mm T+E) on that spur. I would suggest it needs resolving before signing off.
 
We checked sockets, re tightened everything.

Changed mcb to a 20amp.

We are back there tomorrow, will re check.



Sent from my SM-N910F using Tapatalk
 
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk


I am not trying to be difficult but your notes don't make sense. Are you saying the only socket where the Zs is high is at the spur? If so remove the socket and test to the cable.
 
Last edited by a moderator:
Hi,

R1 = 0.29
Rn = 0.30
R2= 1.30

Measured zs 1.48

The socket in question was a spur, the rest of the ring was highest reading 0.42 r1+r2

OCPD 32amp was on the circuit.

Sent from my SM-N910F using Tapatalk


32Amp cb what sort b,c??
 
I am not trying to be difficult but your notes don't make sense. Are you saying the only socket where the Zs is high is at the spur? If so remove the socket and test to the cable.
Hi Murdoch,

That's correct and I will be tomorrow. , I noticed the high Zs prior to board change as I did pre tests and had the discussion with another Sparks who said he notes on his certs rcd protection. I said wasnt correct which brings me here.

I put the the circuit onto a 20amp tybe B until tomorrow as I've got to return with test cert.

Everything else was spot on apart from the other sparks who was there. No test cert, no Sleveing on cpc. No rcd on outdoor lighting, also the swa was just run along garden.

Sent from my SM-N910F using Tapatalk
 
Hi Murdoch,

That's correct and I will be tomorrow. , I noticed the high Zs prior to board change as I did pre tests and had the discussion with another Sparks who said he notes on his certs rcd protection. I said wasnt correct which brings me here.

I put the the circuit onto a 20amp tybe B until tomorrow as I've got to return with test cert.

Everything else was spot on apart from the other sparks who was there. No test cert, no Sleveing on cpc. No rcd on outdoor lighting, also the swa was just run along garden.

Sent from my SM-N910F using Tapatalk

If sockets are rarely used, the contracts are often poor. Plug your tester in and out a few times to see if the reading varies.
 
Thanks Murdoch,

I mention before I have mainly done commercial so old school houses are become the norm.

One thing for sure, if I'm not sure the yellow book appears. I also post here to seek everyone's opinions.

Many thanks

Sent from my SM-N910F using Tapatalk
 

Reply to High Zs on ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top