There was a socket behind a fitted set of draws that I wasn't showen. Had to remove draws and back pannel, was a bugger. I re-tightened connections and it sorted it.


Sent from my SM-N910F using Tapatalk
 
Nice one. Did that sort the high r2 value? What about the spur? Daz
 
The R2 for the ring dropped, also for the spur. I changed the faceplate for the spur and waggo'd the connections behind the draws.

To be honest, it was my own fault. I couldn't find the where the spur was taken from when I tested, I should have known there was another socket but the lady didn't know. Only the husband did when I returned.

Lesson learned.

Sent from my SM-N910F using Tapatalk
 
If you are measuring end to end for the cpcs that R2 reading is way too high, sounds like continuity is breaking down which may well not be at one of the sockets. How old is the circuit, if it goes back to the early seventies the cables may incorporate 1.0 cpcs. Maybe the R2 is correct and the R1 is incorrect. But from your continuity readings the Zs should be approximately 0.58 ohm for any accessory connected direct to the ring final, the Zs of any spurred outlet will depend on its proximity of connection to the ring final.
 
The R2 for the ring dropped, also for the spur. I changed the faceplate for the spur and waggo'd the connections behind the draws.

To be honest, it was my own fault. I couldn't find the where the spur was taken from when I tested, I should have known there was another socket but the lady didn't know. Only the husband did when I returned.

Lesson learned.

Sent from my SM-N910F using Tapatalk


Robo, please don't think I'm having a did, certainly not my intention, but " I waggod the connections" what exactly do you mean by that? as you said you had change the faceplate.
 
Last edited:
Hi Murdoch,

That's correct and I will be tomorrow. , I noticed the high Zs prior to board change as I did pre tests and had the discussion with another Sparks who said he notes on his certs rcd protection. I said wasnt correct which brings me here.

I put the the circuit onto a 20amp tybe B until tomorrow as I've got to return with test cert.

Everything else was spot on apart from the other sparks who was there. No test cert, no Sleveing on cpc. No rcd on outdoor lighting, also the swa was just run along garden.

Sent from my SM-N910F using Tapatalk
not really an issue if it's self burying cable like many use around here :)
 
Robo, please don't think I'm having a did, certainly not my intention, but " I waggod the connections" what exactly do you mean by that? as you said you had change the faceplate.
Hi Pete,

I removed the double socket that was situated behind the draws and joined the cables and fitted a blanking plate.

I thought best, as the socket was not accessible.

Sent from my SM-N910F using Tapatalk
 
Hi Pete,

I removed the double socket that was situated behind the draws and joined the cables and fitted a blanking plate.

I thought best, as the socket was not accessible.

Sent from my SM-N910F using Tapatalk


Right many thanks was a bit confused but not now
 

Reply to High Zs on ring final circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top