I

Innominata

Hi Guys,
I have recently changed the CU in my home in order to have a Napit inspection (not yet a member).I have done a Zs check on all the sockets. Most of the readings are ok but a couple are reading in the region of 1.30 to 1.39 ohms.The MCB is a 32 amp B type.The max allowed from 7671 is 1.44 but do I have to use the 80% rule which would bring the max down to 1.15.The new board is a split load with dual RCD.
many thanks
 
Yes mate 0.8 rule applies sockets giving a high reading check for loose connections if you have not got any would recommend changing the sockets as they are probably at fault.


Hope that helps


Chris
 
Hi Guys,
I have recently changed the CU in my home in order to have a Napit inspection (not yet a member).I have done a Zs check on all the sockets. Most of the readings are ok but a couple are reading in the region of 1.30 to 1.39 ohms.The MCB is a 32 amp B type.The max allowed from 7671 is 1.44 but do I have to use the 80% rule which would bring the max down to 1.15.The new board is a split load with dual RCD.
many thanks

Try putting new sockets on - this has normally sorted out such issues when I've experienced similiar.

One socket where I have recently moved into is within BS on one side and twice the amount on the other side - it's a radial circuit too, hence the sockets at fault.
 
Those Zs results only apply to circuits not protected by RCD, otherwise max Zs for 30mA RCD protected circuit is 1667. Obviously if you've done a Ze and thats fine but find your socket circuit Zs is still high I'd look into it further. instead of testing Zs using a plug in type lead, try taking the socket front off and testing at the connections.
 
Those Zs results only apply to circuits not protected by RCD, otherwise max Zs for 30mA RCD protected circuit is 1667. Obviously if you've done a Ze and thats fine but find your socket circuit Zs is still high I'd look into it further. instead of testing Zs using a plug in type lead, try taking the socket front off and testing at the connections.


is this just for TT system

this is table 41.5 in the regs if anyones interested.

i think with the increased use of rcd protected boards in domestic properties it's important that this particular comparison value isn't overlooked
 
Last edited:

Reply to High Zs readings on ring main in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

For what OCD? There may be other means of over current protection that allow a Zs of0.45 (HRC Fuse?)
Replies
3
Views
376
  • Question
Hi, it turned out to be a very corroded socket outlet, and not a ring. It was two radials. An EICR had been carried out.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top