Hi Guys. Got a kitchen jobs coming up and there is only a 6mm out to hob oven at the mo. New oven specified is 7.4kw and there is 2 single ovens at 3.4Kw each. Total Plate load is 14.2Kw. When I looked at job I thought I would run in another supply. But working it out with diversity all 3 will be 28.52A. I will be putting them on separate isolation switches. Seems close, but ok with regs. Have any of you done similar, Must say I have never heard of an overload issue on 32A cooker circuits before but......./
 
Hi Guys. Got a kitchen jobs coming up and there is only a 6mm out to hob oven at the mo. New oven specified is 7.4kw and there is 2 single ovens at 3.4Kw each. Total Plate load is 14.2Kw. When I looked at job I thought I would run in another supply. But working it out with diversity all 3 will be 28.52A. I will be putting them on separate isolation switches. Seems close, but ok with regs. Have any of you done similar, Must say I have never heard of an overload issue on 32A cooker circuits before but......./

New oven alone is rated at 30a.

I wouldn't do it.
 
Murdoch, there is a 32A MCB fitted, cable is protected against overload. Besides, If they do that that is not my responsibility. I will note on EIC what appliances are connected. Xmas day could be an issue I guess but I will have been paid by then and am not in breach of regs.
 
I would play this one safe and put in another 6mm for the 2 x 3.4Kw single ovens. You said it yourself "Christmas day will be interesting". Nothing wrong with the regs or what everyone has said, but we all know that you will be getting a call the first time the customer has a big family get together to show off their new kitchen for a Sunday dinner when the Yorkshire puddings are flat because the fuse "thingy" keeps tripping.
 
Hi Guys. Got a kitchen jobs coming up and there is only a 6mm out to hob oven at the mo. New oven specified is 7.4kw and there is 2 single ovens at 3.4Kw each. Total Plate load is 14.2Kw. When I looked at job I thought I would run in another supply. But working it out with diversity all 3 will be 28.52A. I will be putting them on separate isolation switches. Seems close, but ok with regs. Have any of you done similar, Must say I have never heard of an overload issue on 32A cooker circuits before but......./
whats the length of run & the cable installation method please...
 
whats the length of run & the cable installation method please...

Good point, its a kitchen so should not be that far away BUT??? :wink:

"The local fuse box is in the double garage just next door to the horse stables some 50m away! Its also a PME, is that a problem?" LOL


For a customer with this amount of ovens and hobs, I dont think I'm too far from my above tongue in check post.
 
I would play this one safe and put in another 6mm for the 2 x 3.4Kw single ovens. You said it yourself "Christmas day will be interesting". Nothing wrong with the regs or what everyone has said, but we all know that you will be getting a call the first time the customer has a big family get together to show off their new kitchen for a Sunday dinner when the Yorkshire puddings are flat because the fuse "thingy" keeps tripping.
and if method C would you stay at 32A?
 

Reply to Hob and 2 single ovens on 6mm cable. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
355
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
908
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
789
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top