M
Meggerman
Hi Guys. Got a kitchen jobs coming up and there is only a 6mm out to hob oven at the mo. New oven specified is 7.4kw and there is 2 single ovens at 3.4Kw each. Total Plate load is 14.2Kw. When I looked at job I thought I would run in another supply. But working it out with diversity all 3 will be 28.52A. I will be putting them on separate isolation switches. Seems close, but ok with regs. Have any of you done similar, Must say I have never heard of an overload issue on 32A cooker circuits before but......./