hi guys
I’m a qualified industrial maintenance elec although not been on the tools for a couple of years. I’m looking on rewiring my home I’ve just moved into. I have been reading up a lot on the regs etc as domestic isn’t my field. Ideally I want to keep the kitchen as it is as it the Only room in the house that doesn’t require decoration therefore kitchen electrics ideally could stay the same. however I noticed the separate hob and oven are both fed off the same 32amp breaker.
I was under the impression these would ideally be separate circuits? It is fed via a 6mm cable from consumer unit to one isolator in cupboard and then 2 x 6mm feeds for both hob and oven.
The hob is rated at 6.4kw and the oven is 4.8kw so overall 11.2kw which equates to 46amp. Correct me if I’m wrong but with diversity would this be overall 20.8amp? (10 + (30% of 36amp) =20.8.
Or is diversity for each appliance seperatly ie HOB with diversity 15 + OVEN with diversity =16 so hob and oven with diversity =31amps.
So Therefore 6mm cable off a 32amp breaker is perfectly fine am I right? Or shall I bite the bullet and put in separate circuits? Just means messing up the kitchen.
So Sorry for the long winded question!!!
I’m a qualified industrial maintenance elec although not been on the tools for a couple of years. I’m looking on rewiring my home I’ve just moved into. I have been reading up a lot on the regs etc as domestic isn’t my field. Ideally I want to keep the kitchen as it is as it the Only room in the house that doesn’t require decoration therefore kitchen electrics ideally could stay the same. however I noticed the separate hob and oven are both fed off the same 32amp breaker.
I was under the impression these would ideally be separate circuits? It is fed via a 6mm cable from consumer unit to one isolator in cupboard and then 2 x 6mm feeds for both hob and oven.
The hob is rated at 6.4kw and the oven is 4.8kw so overall 11.2kw which equates to 46amp. Correct me if I’m wrong but with diversity would this be overall 20.8amp? (10 + (30% of 36amp) =20.8.
Or is diversity for each appliance seperatly ie HOB with diversity 15 + OVEN with diversity =16 so hob and oven with diversity =31amps.
So Therefore 6mm cable off a 32amp breaker is perfectly fine am I right? Or shall I bite the bullet and put in separate circuits? Just means messing up the kitchen.
So Sorry for the long winded question!!!