hi there. was at a job today and the previous electrician has wired a hob in 4 core 2,5mm swa (with separate earth) it is wired in a 3 phase setup with each core being on a 16amcb. as it is a single phase db and setup. is this safe. hob needs a 32asupply
thanks
rob
 
hi there. was at a job today and the previous electrician has wired a hob in 4 core 2,5mm swa (with separate earth) it is wired in a 3 phase setup with each core being on a 16amcb. as it is a single phase db and setup. is this safe. hob needs a 32asupply
thanks
rob

No that is neither safe not compliant, you cannot have a single neutral conductor which is shared by multiple final circuits. For 3x single phase supplies there must be 3x neutral conductors.
The neutral is potentially overloaded as it is at the moment.

Get the installers name and details and report them to anyone who will listen, trading standards, the scams, HSE or anyone else
 
He cant of possibly been an electrician.....The manual says the overall power consumption can be reduced to 4.4KW and minimum circuit breaker size is 20A. Depending on the installation method of the SWA you could put it on a 20A circuit breaker, use three of the cores as LNE and tie the last core down to earth, ditch the separate CPC and make sure the SWA is glanded appropriately with at least one end connecting the armour to earth.
 

Reply to hob wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
395
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
980
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Came across 3No 1ph heaters connected by 2xT&E cables from a 3phase supply on an installation whilst carrying out an EICR few years back...
Replies
9
Views
806
Electric hob/oven range was installed years ago, runs on 2 x B32 MCBs to 'House' (sub)consumer panel, runs to oven on 2 x T&E. Kitchen is being...
Replies
0
Views
294

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top