The power supply is 80W, 1.7A. This is a 15ton rated crane. The brake coil is large and rated at 48VDC...due to its age and poor record keeping, I don't have any more information on the coil. The crane manufacturer couldn't give us anything beyond the voltage. The bridge and trolley brakes, which are considerably smaller, were running the same system and have already been replaced with 48VDC power supplies with success. Operator damage to the crane, including the electrical components for the hoist brake system, has pushed the need for the upgrade. My superiors want to implement a straight 48VDC power supply for both cost and simplicity reasons. I suspected the power supply I had on hand would not be sufficient, but needed to "prove" that before a larger one was ordered. I don't have any science to back my belief that it's not large enough or that a straight power supply system will even work. Until I show that this won't work, going with an updated version of the old method won't be considered...especially since it works with the bridge and trolley brake coils.
That is correct, it was not a true DC system. It was rectified from a 480VAC primary/48VAC secondary transformer. Yes, it is a pure DC power supply.
[automerge]1598442004[/automerge]
Continuing with the rectified AC vs true DC with the power supply...doesn't the DC power supply do exactly what the other components were doing? The DC power supply transforms the incoming AC to the usable AC voltage level, then rectifies that AC voltage level to DC, then passes the voltage through a filter to smooth out the waveform. All this happens inside a single component. What am I missing that makes this process different from the old supply system?