Hi,

What size supply would you install for a kind of wendy house in the garden that's going to be used as an office for 2 or 3 people.

around 6 sockets and a double fluorescent. They'l probably be plugging in a 2kw heater at some point when it gets to winter.

Is a 32A feed on 4mm swa a bit overkill? Knock it down to a 2.5mm on a 20A? what would you do? probably not much cost difference.

Was planning on running a 16A radial socket circuit and a 6A radial for light.

Thanks
 
ah yea it would have to be a 6mm for a 32A supply to be under 6.9v. i'l re measure the run perhaps i was being a bit generous, it might be more like 15M.

Don't forget that your total distance is measured from the intake, not the hole in the wall where the cables comes out into God's fresh air.

6mm 3 core IMO. That will mean you can boil a kettle and have the heating on at the same time!
 