Hi i have a homework question i am not sure about the question is (word for word)

"State the requirements of bs7671 for pfm may not permit the use of a bs 3036 semi enclosed device as a means of over current protection for this installation"

the only reason i can think of is that the breaking capacity might not be high enough or the fusing factor might be too high.
the pfc on the installation is quoted as 1.2 KA but im sure that the breaking capacity of a 3036 is 1-3 KA so it should be ok but as i said i am totally stuck at where to look in the regs the closest i can find is reg 432.1 but im not sure.

Can any one help
 
What you've written there is what I'd be going for, Baker. The first paragraph in Reg. 434.5.1 sums it up quite nicely, I feel.

And just expanding a little on what you've correctly said, there, is that depending on the device designation / type of BS 3036 fuse, its Icn rating may actually be less than the Pfc. That you mention this shows that you've clearly understood what was being asked.

Perhaps have a look at Table 7.2.7(i) in the OSG too.
 

Reply to Homework in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top