Just a quick questiin can i use a 3 amp for a 2A fused connection unit the factory manuel is saying 2 amp full stop is this 100% or can i use a 3 amp i would of thought this would be sufficiant and then wired to a 6 amp breaker? Never done a alarm system before so making sure as dont want to pop any components
 
If the manufacturers specify 2 amp then yes that is the size you need to fit, fitting higher could damage the electronics under overload or fault conditions before the fuse operates. The 6amp at the breaker is protecting the cabling you wire to the fused spur... are you sure the 2amp is not applying to internal fuses in the panel itself, usually they do not ask for a 2amp in the fused spur supplying power to the unit thus 3amp will be fine... open the panel up, normally there is a fuse as part of the incoming terminals.
 
If you are a spark, best "open" up your profile so people can see your experience

As for fuses, as others have pointed out, you can buy 2A fuses (and others) so buy a few packs for your stock...
 
honeywell are wrong saying to use a sFCU. should be unswitched. so they're probably wrong about the fuse size also. i've been installing alarms since 1981 and without exception, all call for a 3A unswitched FCU.
 

Reply to Honeywell 2 amp fused connection unit in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
321
All socket outlets up to and including 32A (which are commercial, not domestic) are required to be 30mA RCD protected. By the sounds of it you...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top