looking at tranformer 300va and 12volt out 1.omm2 t+e cable get really hot but unable to get at lights lv 20w halogen dicronic will need abit of scaffold would this inicate a possible loose connection from light to transformer therefore making the cable hot but otherwise transformer looks ok 230v 12v ect in out
 
looking at tranformer 300va and 12volt out 1.omm2 t+e cable get really hot but unable to get at lights lv 20w halogen dicronic will need abit of scaffold would this inicate a possible loose connection from light to transformer therefore making the cable hot but otherwise transformer looks ok 230v 12v ect in out
is the 1.00 feeding just one lamp or multiple
if more than one the cable will need upgrading as the current will be through the roof
 
300va at 12volt i agree looking at 25amp there you would need a 6mm at least which wont fit the terminals unless it has multiple outputs and still cables need to be as short as possible as volt drop becomes an issue, does seem either way to be a poor design and shoulb be scrapped or re-wired with a thought to transformer position and length of cables outgoing.
 
wait theres more 1mm t+e feeding one 300va and looped out to feed a 150 va transformernext to it then the 150va lights are one a spuspened track has 4 x 12volt 20w lamps in and then the 300va has 6 x 12volt 20w lamps in and 6 decking kind of 12v lights in the laminate flooring but again these are 20 watt lamps but the cable that i acn only find hot is the 1.0mm that goes to the suspended track lights could it be a bad neutral do you think ?
 
wait theres more 1mm t+e feeding one 300va and looped out to feed a 150 va transformernext to it then the 150va lights are one a spuspened track has 4 x 12volt 20w lamps in and then the 300va has 6 x 12volt 20w lamps in and 6 decking kind of 12v lights in the laminate flooring but again these are 20 watt lamps but the cable that i acn only find hot is the 1.0mm that goes to the suspended track lights could it be a bad neutral do you think ?
The 230v supply loop is adequate between the ingoing side of the transformers but its the outgoing 1mm thats your problem, basic ohms law on this one im afraid 6x20w =120w thus 120w divided by 12v is 10amps then the length of the cable to take into account and at 12v you would be subject to volts drop in a short run hence your hot cable. DEpending on length of run you may require 4mm or 6mm on outgoing side to feed track.
 
Last edited by a moderator:

Reply to hot cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top