Have a 3 phase installation 3 phases plus the neutral are fed by 25mm cables into 63A circuit breaker then all split of into the 3 RCD's with 10mm cable inc the N lives are all warm but Neutral is hot checked screws for tightness etc no circuit is reading more than 41 Amps . Any ideas???????????
Cheers
Mayfair
 
Just a shot in the dark, does the neutral pass through a metal casing by its self. say a hole in trunking.If it does you may be producing eddy currents which will produce heat or check you are getting a 3phase and neutral supply at your incommer you may have lost your incoming neutral. I hope this helps you out.
 
Are the 10mm cables single? Bunched? In free air? Containment?

BS7671 allows a current carrying capacity of 42amp to 59amp depending on these factors (assuming cable at the 10mm stage is non armoured single core..)

Seeing as how the over current device is 63 amp I would consider this to be a potential danger and so the best action to take may be to increase the 10mm conductors to 16mm or better still 25mm.



Need more info to be as accurate as poss, but it appears that the cable are near it's peak tolerance if the lines are warm and neutral is hot.

Are the circuits csa 10mm?



Hope this makes sense...
 
Last edited:
Are the 10mm cables single? Bunched? In free air? Containment?

BS7671 allows a current carrying capacity of 42amp to 59amp depending on these factors (assuming cable at the 10mm stage is non armoured single core..)

Seeing as how the over current device is 63 amp I would consider this to be a potential danger and so the best action to take may be to increase the 10mm conductors to 16mm or better still 25mm.



Need more info to be as accurate as poss, but it appears that the cable are near it's peak tolerance if the lines are warm and neutral is hot.

Are the circuits csa 10mm?



Hope this makes sense...
25 mm singles into the mcb 63A then when i split it into the 3 rcd's got 10mm singles so they are about 20cm long to the rcd's and they are warm but noting to write home about as it was 33 deg here today, the room they are in was 37deg.
But the N that has been fed into choc block and split to the two pole rcd's all on 10mm........ is notably hottish........ all csa halogen free decent quality cable make any sense m8 btw free air that is in the dis panel
 
Last edited by a moderator:
a short bit of 10sq feeding the rcds and final circuits- ya?


measure the N current anyway as already said

for harmonic currents you need 'true rms ' reading

dunno if it's an issue -any computers?
 

Reply to Hot Neutral in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
983
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
534
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
267

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top