Hi Guys
Have a 3 phase installation 3 phases plus the neutral are fed by 25mm cables into 63A circuit breaker then all split of into the 3 RCD's with 10mm cable inc the N lives are all warm but Neutral is hot checked screws for tightness etc no circuit is reading more than 41 Amps . Any ideas???????????
Cheers
Mayfair
 
All the computers and all other loads need to be on when you current clamp the neutral conductor to give you a realistic reading.

You may find you will at least need to increase the size of the neutral conductor as a minimum.
 
think so - oversize the neutral on 3-phase 4-wire if neccessary


the ordinary clamp wont measure harmonic currents although i think overcurrent protection (if used on a neutral) would operate


may not be that anyhow
 
Last edited by a moderator:

Reply to Hot Neutral in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
983
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
534
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
267

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top