installed a tub for m8 (second hand).

switch on tub runs for about 10 seconds then trips.

clamped up draw initially 3.3A -12.2A when heater kicks in.

disconnected heater unit IR test 400M ohms, 23 ohms heater resistance.

disconnect pump one hot tub will stay on, disconnect heater & leave pump one on hot tub will run but did trip once after about 20 mins.

pump one
checked capacitors 16m farad good, 40m farad good. checked windings brown to blue 11.08 ohms, black to blue 11.10 ohms. IR test to earth 400M ohms.

disconnect plugs for ozone still trips, blower still trips & light still trips.

my findings hot tub turns on timer runs down pump one starts draw around 3amps heater kicks in around 12amps then trips after about 2-3 seconds later thinking I have a earth fault under load or am I missing something ?
 
Guessing it's the 30mA RCD that trips - ramp test it? Measure the earth leakage at the tub. When heater IR tests were done, was the tub in working condition with water etc. Results so far seem to point to heater, but that's not backed up by the IR test :( . What is the earthing arrangement (just interested) and has the tub been working ok for a while, or is this maybe why the previous owner sold it on?
 
installed a tub for m8 (second hand).

switch on tub runs for about 10 seconds then trips.

clamped up draw initially 3.3A -12.2A when heater kicks in.

disconnected heater unit IR test 400M ohms, 23 ohms heater resistance.

disconnect pump one hot tub will stay on, disconnect heater & leave pump one on hot tub will run but did trip once after about 20 mins.

pump one
checked capacitors 16m farad good, 40m farad good. checked windings brown to blue 11.08 ohms, black to blue 11.10 ohms. IR test to earth 400M ohms.

disconnect plugs for ozone still trips, blower still trips & light still trips.

my findings hot tub turns on timer runs down pump one starts draw around 3amps heater kicks in around 12amps then trips after about 2-3 seconds later thinking I have a earth fault under load or am I missing something ?
Well if you are getting those sort of insulation resistance readings it no wonder the tub is tripping out. What is actually tripping CB or RCD?
 
Guessing it's the 30mA RCD that trips - ramp test it? Measure the earth leakage at the tub. When heater IR tests were done, was the tub in working condition with water etc. Results so far seem to point to heater, but that's not backed up by the IR test :( . What is the earthing arrangement (just interested) and has the tub been working ok for a while, or is this maybe why the previous owner sold it on?

good idea I will ramp test RCD & check the leakage of the trip with tub on & see the spike. will check Monday, did not think RCD as know the house no issues with RCD to date. TNCS
 
my thoughts at guess at one point heater had small crack in when heating let water past but heater has water around it all the time so can't see it especially with the IR value being good.
 
Well if you are getting those sort of insulation resistance readings it no wonder the tub is tripping out. What is actually tripping CB or RCD?

Hi Pete
VIR
230 V
10.3 I
23.3 R
sorry am I having a blond moment heater is 2.5kw.

400M ohms IR test to earth good
23.3 ohms heater continuity
did you spot something that in the above that I may have missed ?
 
good idea I will ramp test RCD & check the leakage of the trip with tub on & see the spike. will check Monday, did not think RCD as know the house no issues with RCD to date. TNCS
Hi - understand, I have seen where RCD is a bit sensitive and a few mA is already there from other appliances on the circuit (?).
 
Hi - understand, I have seen where RCD is a bit sensitive and a few mA is already there from other appliances on the circuit (?).
be quite honest there is only 3 items on this side of the board & hardly any equipment installed apart from usual fridge wash machine few sockets, not really much in Bungi
 

Reply to hot tub fault tripping after switching on in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top