hot tub fault tripping after switching on | Page 2 | on ElectriciansForums

Discuss hot tub fault tripping after switching on in the UK Electrical Forum area at ElectriciansForums.net

marc8

-
Joined
Jun 10, 2012
Messages
718
Reaction score
173
Location
Essex
installed a tub for m8 (second hand).

switch on tub runs for about 10 seconds then trips.

clamped up draw initially 3.3A -12.2A when heater kicks in.

disconnected heater unit IR test 400M ohms, 23 ohms heater resistance.

disconnect pump one hot tub will stay on, disconnect heater & leave pump one on hot tub will run but did trip once after about 20 mins.

pump one
checked capacitors 16m farad good, 40m farad good. checked windings brown to blue 11.08 ohms, black to blue 11.10 ohms. IR test to earth 400M ohms.

disconnect plugs for ozone still trips, blower still trips & light still trips.

my findings hot tub turns on timer runs down pump one starts draw around 3amps heater kicks in around 12amps then trips after about 2-3 seconds later thinking I have a earth fault under load or am I missing something ?
 
Had a similar problem on a Sauna some years ago, IR test all good but within seconds of the heaters kicking in the RCD would kick out.
Turned out that it had been sitting in a warehouse unused for a while & the elements had got damp in them.
 
Had a similar problem on a Sauna some years ago, IR test all good but within seconds of the heaters kicking in the RCD would kick out.
Turned out that it had been sitting in a warehouse unused for a while & the elements had got damp in them.
Hi Thanks for that specialist
as above I will disconnect heater & power supply from tub probably use a 16amp CB inline at tub whilst I am there disconnecting & then turn on heater direct through 16amp CB, hopefully will trip or heat up.
 
Hi Pete
VIR
230 V
10.3 I
23.3 R
sorry am I having a blond moment heater is 2.5kw.

400M ohms IR test to earth good
23.3 ohms heater continuity
did you spot something that in the above that I may have missed ?
No Marc I misread your post, thought you had said you had measured 400 ohms IR missed the dirty great capital M, sorry for any confusion
 

Reply to hot tub fault tripping after switching on in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top