installed a tub for m8 (second hand).

switch on tub runs for about 10 seconds then trips.

clamped up draw initially 3.3A -12.2A when heater kicks in.

disconnected heater unit IR test 400M ohms, 23 ohms heater resistance.

disconnect pump one hot tub will stay on, disconnect heater & leave pump one on hot tub will run but did trip once after about 20 mins.

pump one
checked capacitors 16m farad good, 40m farad good. checked windings brown to blue 11.08 ohms, black to blue 11.10 ohms. IR test to earth 400M ohms.

disconnect plugs for ozone still trips, blower still trips & light still trips.

my findings hot tub turns on timer runs down pump one starts draw around 3amps heater kicks in around 12amps then trips after about 2-3 seconds later thinking I have a earth fault under load or am I missing something ?
 
Just re read the OP and noticed it is second hand do you know what chemicals the previous owner has been using, if it was chlorine then you may find that a seal has rotted and leaking water into something when it is running
Bromine is much more friendly and doesn't cause as much damage as chlorine
 
Just re read the OP and noticed it is second hand do you know what chemicals the previous owner has been using, if it was chlorine then you may find that a seal has rotted and leaking water into something when it is running
Bromine is much more friendly and doesn't cause as much damage as chlorine
thanks will ask tomorrow when I am going round to take a look at the rest
 
Hi all
Well back today electrically disconnected heater from tub & installed link through fused spur to heater, turned on heater working but with earth clamp round L/N supply to tub 50.1ma whilst heater on.
So my guess although heater unit is heating & the IR test 400M ohm to earth & continuity of element 23.3 ohms.
The heater still has a problem any other ideas would be welcome before I swap heater unit ?
 
Personally I'd make sure there was plenty of water in it & then let it run for a couple of hours to let the element boil the moisture off. Just keep a close eye on it & monitor the leakage current.
 
Expected it to go up first & then start dropping.
A few years back, I had a call to look at a Commercial cooker that had been stored in a garage for months while waiting to be installed.
When it was installed in the old peoples home, it tripped out when the oven was used.
Sparky on site disconnected & Meggered, no fault found. But it still tripped the RCD, So I got sent to look at it. I disconnected the oven elements & made up a cable to go to a non RCD supply & left it run, after a few minutes I tested the element & found leakage to Earth. We let it sit & cook while monitoring it, took over 4 hours before it was OK to use.
Has the increase in leakage started to level off yet ?
 
Expected it to go up first & then start dropping.
A few years back, I had a call to look at a Commercial cooker that had been stored in a garage for months while waiting to be installed.
When it was installed in the old peoples home, it tripped out when the oven was used.
Sparky on site disconnected & Meggered, no fault found. But it still tripped the RCD, So I got sent to look at it. I disconnected the oven elements & made up a cable to go to a non RCD supply & left it run, after a few minutes I tested the element & found leakage to Earth. We let it sit & cook while monitoring it, took over 4 hours before it was OK to use.
Has the increase in leakage started to level off yet ?
Only climbing moment ago 116ma
 
That sounds more like the element has been under water, rather than damp. Wonder if it came from an area that was flooded last year & that's why it was sold off.
Your friend may end up having to bite the bullet & fork out for a new element.
What's that been ? About an hour now, would have expected it to have started levelling off by now & then slowly decreasing over time.
 
That sounds more like the element has been under water, rather than damp. Wonder if it came from an area that was flooded last year & that's why it was sold off.
Your friend may end up having to bite the bullet & fork out for a new element.
What's that been ? About an hour now, would have expected it to have started levelling off by now & then slowly decreasing over time.
Over an hour now, ordering a new element today so hopefully by thursday will be fixed.
THanks for the help everyone
 

Reply to hot tub fault tripping after switching on in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top