Hey guys
This may have being touched on before.
I have got to install a 32amp Hot tub for a customer.
The installation is a dual RCD board
TNCS
All bonding in place.
I am going to install a 6mm 3core armoured surface cleated to garage wall and the hot tub will be installed behind the garage where I will put in a 32amp rotary isolator.
I have heard many discussions on weather acceptable to export the PME and you should TT the hot tub in case of loss of neutral and the potential dangers that could arise, now I’m not sure if the hot tub is class 2 although speaking to the manufacturer they have said the frame is metal but the actual surroundings and the centre are all plastic.
What’s your thoughts and past experience on what you do with these installs
Thanks
This may have being touched on before.
I have got to install a 32amp Hot tub for a customer.
The installation is a dual RCD board
TNCS
All bonding in place.
I am going to install a 6mm 3core armoured surface cleated to garage wall and the hot tub will be installed behind the garage where I will put in a 32amp rotary isolator.
I have heard many discussions on weather acceptable to export the PME and you should TT the hot tub in case of loss of neutral and the potential dangers that could arise, now I’m not sure if the hot tub is class 2 although speaking to the manufacturer they have said the frame is metal but the actual surroundings and the centre are all plastic.