Guest viewing limit reached
devonsparky
This is a follow up to a thread I started yesterday.
I have been working all day installing a hot tub situated outside on a patio slabbed deck.
Contrary to what I was told, it was TN-C-S supply so here is how I have wired it.
  • From Henly blocks - 25mm tails to a one way board (Main Sw RCCB - 50A MCB)
  • 10mm 3 core SWA from board to 63A rotary isolator and from rotary isolator to hot tub
  • Earth rod with 10mm G/Y back to one way board and then used one core as an earth to the hot tub and connected the armour to the earth bar too.
Time beat me today so I have not connected into the Henly blocks yet and tested .......................... Is this how you guys would have done it. 10 years in the game and an approved electrician and it's still nice to get feedback off of this forum !! ha ha
I've got one of these to do this week, same tncs I'm also fitting a earth rod but was going to fit it near the tub, I thought closer to tub the better cus less potential difference within the earth? Or have I just made myself look really stupid?
nope , youre right.
i would have fitted the earth rod within 2-3 metres of hot tub with earth cable connected to rotary switch.
My earth rod is in the only suitable position ............... it is roughly 4-5 metres away from the tub.
Ideally within 2-3 but surely this is good enough. My head is ready to explode !! I'm a pretty experienced electrician but this install has had me researching the regs/guidance notes/forums etc to make sure it is all done correctly. Looking forward to getting it tested and certified and getting out of there. ha ha
How can these 4-8 week courses make someone a Part P sparky when even the most expereiced sparks are always learning !!
Who's Buff ?
rcd can be at the mains or local to hot hub if using swa , either is ok.
yes , connect swa and earth conductor together at the CU.
The whole hot tub installation is therefore on TT.
no its not , all you've done is connect your earth rod conductor back to the MET of a TNCS supply , which doesnt achieve that much.
the earth rod cable should be connected to the end of the circuit at the rotary switch for the biggest benefits.
The earth rod cable goes back to the MET of the one way fuseboard I have installed specifically for the hot tub. Surely this makes this fuseboard TT as its L + N comes off of the Henly blocks.
ah , didnt realise you werent taking an earth from the MET for the one way CU , my bad.
what was your earth rod loop reading out of interest ?
ha ha ................... No worries Biff55 !
I haven't finished the job yet so still have to put my one way fuseboard up yet ................ therefore I haven't done any testing yet.
I'm thinking if the earth loop reading needs to come down I can still stick another rod in from the rotary isolator.
I will post the readings if you are interested once I finish the job.
(Is it just me who feels like they are bordering on the side of electrical geek by spending the evening in this forum ?? lol)
Okay, going to stick my neck out here....
why haven't you used the perfectly good earthing system provided (TNCS) and ... exported it?
bayonet fixed
I've started to spend a lot if time on here, nice to get other peoples view on stuff, as there's no one to chat about stuff when your out there. Not just make sure your not breaking the regs it's just nice to see how others would do things.
Hot tub installation !
devonsparky,
SPARTYKUS,
