ian w j

Help Needed !!
The wife has just purchased a hot tub off eBay! I am a spark but not a bright one!! I was just looking into what's required for the supply and they are stating 8-10kw load 32-40amp supply. To an an isolator and have Rcd protection.. yeah ok so far. I know about the zones regarding position of isolator and other equipment as per the regs, but I am stressing about the demand and diversity of the installation. I'm going to do the work and get a friend to pass it off and certify.

Currently I have a 100amp single phase domestic supply.

The dis board has:
2 x 32a rings
1 x 32a radial cooker supply with single socket(cooker is 13a socket)
3 x 6a radial light
1 x 6a smoke
1 x 6a water(no immersion heater)

I've done a diversity calc not taking into account the smoke and the heating time clock and come up with 103amps using a 32 amp supply to the hot tub.
My supply is 100amps !! Is this right??
 
The fuse is deffo 100amp bs1361 ,unless anyone knows the resistance for a 60amp 80amp 100amp! The fuse inside is fully enclosed !! With all the lights,4 tv's, fridge freezer oven,half the sockets with lamps on its about 60 amp according to my clip on, that minus washer and dishwasher and dryer and the hot tub
 
The fuse is deffo 100amp bs1361 ,unless anyone knows the resistance for a 60amp 80amp 100amp! The fuse inside is fully enclosed !! With all the lights,4 tv's, fridge freezer oven,half the sockets with lamps on its about 60 amp according to my clip on, that minus washer and dishwasher and dryer and the hot tub

I think what has been forgotten is that your hot tub will only likely ever pull 32A when first heating up. It'll just be ticking over keeping temperature, etc. for the rest of the time. If you are that worried about it turn everything else off when you first power it up!
 
The fuse is deffo 100amp bs1361 ,unless anyone knows the resistance for a 60amp 80amp 100amp! The fuse inside is fully enclosed !! With all the lights,4 tv's, fridge freezer oven,half the sockets with lamps on its about 60 amp according to my clip on, that minus washer and dishwasher and dryer and the hot tub


Please be reminded that if your reply can't help the original poster, it may be seen as pointless and taking the thread off topic. Please make sure what you are about to post is in-keeping with the forum rules, specifically the "be nice" rule. Just be nice and helpful (even to new members) or don't reply at all please. Also note that we urge all members, regular or new, to report any posts that are off-topic, pointless or offensive.


Good luck fella (big kiss and cuddle)
 
Surely when the supply company connect up they have to clearly identify the current rating of the supply! The seals aren't meant to be cut off to find this out when you do an Niceic test are they?

If you look really close you'll notice that there aren't any seals ;-)
You'll have to break them anyway to verify the fuse rating.
 
The fuse is deffo 100amp bs1361 ,unless anyone knows the resistance for a 60amp 80amp 100amp! The fuse inside is fully enclosed !! With all the lights,4 tv's, fridge freezer oven,half the sockets with lamps on its about 60 amp according to my clip on, that minus washer and dishwasher and dryer and the hot tub
Are they all heat lamps?!...

Time to look at some energy saving lamps, equipment, accessories etc etc...
 
The fuse is deffo 100amp bs1361 ,unless anyone knows the resistance for a 60amp 80amp 100amp! The fuse inside is fully enclosed !! With all the lights,4 tv's, fridge freezer oven,half the sockets with lamps on its about 60 amp according to my clip on, that minus washer and dishwasher and dryer and the hot tub

Only in your wildest dreams!!!
I'd sling that amp clamp in the bin if i were you if it's reading 60A for what you have stated were the circuits being used....

Seems that you can't be bothered to listen to what anyones trying to tell you. Your DNO cut-out fuse carrier is just that, a carrier, it can hold a 60A, 80A or a 100A BS 1361 or now a BS 88 cartridge fuse..... So what make you so sure that it's 100A then??
 
The last time I had a clamp on a cable that was measuring around 60A was a couple of weeks ago. Was going between 55 and 68 amps over about 10 minutes. This was a restaurant with all lighting on, none of it energy saving, the kitchen in full swing, and the 16mm tails were warm to the touch.

Just saying.
 
The current 'professional electrician' free magazine has a write up on supplying hot tubs from PME supplies, quite a useful read for anyone who does these.
(Only cos it backs up what I've said about the subject previously ;) )
 
Only in your wildest dreams!!!
I'd sling that amp clamp in the bin if i were you if it's reading 60A for what you have stated were the circuits being used....

Seems that you can't be bothered to listen to what anyones trying to tell you. Your DNO cut-out fuse carrier is just that, a carrier, it can hold a 60A, 80A or a 100A BS 1361 or now a BS 88 cartridge fuse..... So what make you so sure that it's 100A then??
Welcome back fella, we have missed you
 
Please be reminded that if your reply can't help the original poster, it may be seen as pointless and taking the thread off topic. Please make sure what you are about to post is in-keeping with the forum rules, specifically the "be nice" rule. Just be nice and helpful (even to new members) or don't reply at all please. Also note that we urge all members, regular or new, to report any posts that are off-topic, pointless or offensive.


Good luck fella (big kiss and cuddle)
I clearly missed the memo about forum members having to be touchy-feely!?
 

Reply to hot tub supply in domestic dwelling 32A, 100A supply in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top