Guest viewing is limited
Im after some advice regarding the earthing of a 32Amp hottub. I've yet to install one and am dubious about the risks associated.
The supply is T-N-C-S.
My plan is to put a seperate supply direct from origin via henleys to a 50amp MCB. 10mm 3c SWA approx 25m to a small wooden workshop. Within the workshop I'm locating a seperate DB with 30mA RCBO to supply small power / lighting within and the 32Amp hot tub sited on patio.
6mm 3c swa to rotary isolator. At this point I'm going to lose the supply armour via stuffing gland and internal cpc via wago. I was then going to install an earth rod connected to the load swa cpc and armouring upto hottub.
Can anybody see any issues with my scenario or further advice?
Not entirely correct, in practice there may be an indirect requirement.
The reason DP RCBO's are sometimes required on TT systems is because an S type time delayed RCD is often used as a main switch. This is a preferred arrangement because it provides back up earth fault protection where there is total reliance on the operation of an electronic RCD device. If a single pole RCBO is used it will not disconnect the neutral in the event of an earth fault on a final circuit, which could then result in the RCD main switch operating disconnecting the entire installation. If a DP RCBO is protecting the final circuit that wont happen, the affected final circuit will be completely disconnected. This would be a breach of the regulation requiring a single fault not to result in complete power failure.
The same scenario would not be the case if a dual RCD board is in use with SP MCB's and an up-front S type main switch, as the dual RCD's would both be DP.
Regarding the OP , the use of a TNCS system is permitted for a hot tub arrangement and I would have no issue using it. As already stated, the presence of two separate earthing systems may create more of a hazard.
Also a regulation often overlooked is the presence of external lights adjacent to the tub, there are strict regulations on where lighting can be installed which need to be considered and often aren't with domestic installations.
There is no requirement in BS7671 for double-pole circuit protection on a TT earthing system. I understand your argument for the single fault scenario but nevertheless it is not required.
If you have loads of 3 core already to hand it makes sense, otherwise it is easy and cheaper to buy 2 core SWA by the meter, etc, from any of the usual suppliers on-line or at trade outlets.
The usual reason for going 3-core on single phase are one or more of:
  • Not meet the Zs for disconnection times for sub-main OCPD due to high R2
  • Armour not meeting adiabatic limit for fault clearing
  • Not meeting 10mm copper equivalent bonding for extraneous conductive parts on TN-C-S
There probably are other things I have missed and other folk will point out tomorrow...
Seems a waste of copper! If you have a spare core with no other use then put it in for parallel earth on the SWA.
Where do you plan on putting the earth rod connection, in to the isolator switch box?
You should be thinking of the poor sod who follows you years later trying to sort something out - make the design clear and properly label things so anyone else needing to do work can see exactly what is being done (and ideally why) from a simple inspection of it.
I understand the difference between a 2c and a 3c cable and the various reasons stated. Its not a 50mm its a 6mm. The cable run is local and cable readily available. I dont consider wastage or cost an issue tbh for such a short run.
I was simply reffering to the comment of 2 x earth sources within the same enclosure. By losing the cpc at DB it would eliminate that.
The earth rod will be located adajcent to the isolator.
As for inspection and testing I'd approach that isolator 2m from a hottub and clearly see the reason they've converted to a TT arrangement. Possibly applaud the effort made as they've understood the risks exporting a TNCS arrangement.
Its all very well criticising but not one person has stated a different approach regarding the TT. (I would rather not TT the workshop DB.)
There is not a direct requirement I agree. But if a T/D RCD main switch is fitted with SP RCBO's it will not comply because a single fault on a final circuit may still take out the main switch. That does not comply. So where a T/D main switch is fitted with RCBO devices DP RCBO's are required to comply with the regulations. SP RCBO's would be a departure.
Regulation 531.2.2.201
Regulation 531.3.1.201
No requirement to disconnect Or switch the neutral under fault conditions or for protection against electric shock for TT or TN systems unless additional measures are required by part 7 such as caravan installations etc
I wouldnt be applauding anything about the proposed plan of disconnecting the CPC at the isolator and connecting an earth rod.
I would not be converting any part of the installation to TT if possible, the TNCS earth will always be a better earth, I would prefer to install earth electrodes connected to the MET to guard against the possibility of a lost PEN.
They will eventually, hopefully, actually bring this in to our regulations.
You are not exporting TN-C-S, you are using a cpc which is derived from a TN-C-S source.
Yes my error
I agree that i don't particularly want to use a TT with a less reliable earth. However i presumed thats standard practice regarding a hottub outside the equipotential zone. Thats why I've started the post for advice.
Could i use theTNCS upto the hot tub and just connect an earth rod at the workshop DB as backup? Is this what your immplying?
Have you checked the regulations for outdoor swimming pools as they are the closest thing to an outdoor hottub?
I'm not implying anything, I'm sharing my opinion that earth electrodes connected to the MET are the best solution.
I'm certainly not suggesting 'just connect an earth rod' because a single earth rod is never enough to provide a reliably low Ra.
I guess the real issue is not so much the reliability of the TT's earth as such (you could have two rods in different areas and two wires so no single point of failure) but making sure it will reliably disconnect on a fault.
With a TN-S / TN-C-S you have RCD, magnetic, and thermal actions that will all ultimately trip the breaker, but on TT only the RCD will realistically do it as you simply won't have a low enough Ze.
But if you go for the more traditional TT set up for the workshop with a 100mA S-type RCD incomer and then 30mA RCBO for each circuit then you are not relying on a single RCD to disconnect on a fault.
The subject of TN-C-S and outdoor stuff comes up regularly and always prompts a bit of a heated debate as there are sound points and strongly held beliefs on many fronts! So far hot tubs and similar have not really been a comon subject, but the risk of EV changers for cars had mandated something must be done, but not clear yet if a cheap and easy solution outside of EV kit is going to be widespread.
For now it is "to TT, or not to TT, that is the question"
Could i use the TNCS up to the hot tub and just connect an earth rod at the workshop DB as backup? Is this what your immplying?
A single standard rod will never get a low enough impedance to pull down a PME fault voltage far enough. If you had a couple of rods around the hot tub zone (or some buried mesh, etc) you might be able to keep the step/touch potential gradient down but that would be a major design effort (needing the sort of modelling software they use for lightning protection and earth validation for major installations) to establish its effectivness.
What we need is a change of attitude towards protection against a PEN fault/earthing/taking responsibility.
Foundation trenches are a great place for a horizontal electrode, an earth connection to the steel reinforcing is also a great electrode. Its already normal for the reinforcing to be connected to the elctrical earth on big buildings, how much of a change would it be to make this common practice for small buildings?
If building regs changed to require 2 connection points to the rebar to be made available for earthing when any foundation or slab is cast then I think we could easily achieve good earth connections for all installations.
Obviously this wouldn't immediately affect existing buildings, but that's not a reason not to do it for new buildings, and slowly as extensions are built etc the overall effect would be to make everyone safer.
Single pole rcbos would not be a departure as there is no requirement which specifies them.
You are both missing the point. SP RCBO's would only be a departure where a T/D RCD main switch was installed, not because the regs state SP RCBO's are not permitted, but because a single fault would probably still trip the main RCD. If someone said they were protecting the entire installation with a single RCD and MCB's you would say that is non compliant, the effect of a fault on a final circuit would be exactly the same as a T/D RCD with SP RCBO's.....total loss of power, therefore that arrangement is non compliant as well for the same reason.
I know there was another reason:
  • High integrity earthing (high leakage currents) with two CPC
Now can I turn this in to a Spanish Inquisition sketch?
I do get your point, mearly pointing out what the regulations say about the neutral on TT and TN systems.
However there’s a difference between a departure and a non compliance, your example is not a departure as to depart is to afford the same degree of safety etc etc.
Completely agree that you would want selectively between rcd’s
Agreed I used the wrong terminology....not a departure but definitely a non compliance IMO, been too many weeks not working!
Northants
United Kingdom
Hot tub - TN-C-S
snipersmith87,