Hi Folks,
have been asked to remedy problems created by an 'electrician' who left his spurs and saddlebag in the understairs cupboard...
:cowboy:

Here is what there is:
Its a TT system
At the CU end is a 40A 30mA RCD, 4mm SWA run of approx 8 meters to outbuilding.
In the outbuilding a 63A 30mA RCD 2x 20A and 1x 6A mcbs.
One of the 20A mcb's feeds a 13A fused spur which has a length of 2.5mm flex intended for the hot tub connection.
The other is for sockets and the 6A is for lights.

My plan is to replace the 40A RCD with a 63A. Replace the 4mm SWA with 6mm (as per manufacturers info)
Put a 63A 100mA RCD in the outbuilding.
Replace the 20A mcb with a 32A and ditch the fused spur for a 32A rotary isolator.

Now my question is, do I need a separate earth for the outbuilding as the house is already TT? The earth spike is in the garden about 5 meters from the outbuilding and about 2 meters from the tub.

Edit.....post removed,probably a bit harsh.
 
Last edited by a moderator:
Fair enough. I think I should of thought it through a bit more before posting my question. So I will today I will decide on the discrimination aspect, which came about partly due to previous 'electrician' installing the two RCD's.

Could I therefore get back to the original question, please.
Do I need another earth spike as main house TT spike is so close to the outbuilding/hot tub?
 
Fair enough. I think I should of thought it through a bit more before posting my question. So I will today I will decide on the discrimination aspect, which came about partly due to previous 'electrician' installing the two RCD's.

Could I therefore get back to the original question, please.
Do I need another earth spike as main house TT spike is so close to the outbuilding/hot tub?

Pick one up from wholesalers and test at sub board if you dont need it take it back
 
Fair enough. I think I should of thought it through a bit more before posting my question. So I will today I will decide on the discrimination aspect, which came about partly due to previous 'electrician' installing the two RCD's.

Could I therefore get back to the original question, please.
Do I need another earth spike as main house TT spike is so close to the outbuilding/hot tub?



So what is the current Ra value that you are seeing with the existing earth rod?? If it's a completely Naff value and/or gained from one of those thin 3/8'' twigs, then it would be better to replace altogether. If it's a decent sized rod that still has a viable screw thread, then couple another rod on to it. Or you can drive in another 2 X 1.2M coupled rod making sure you are at least 3 metres or more distant from the existing rod. Depth is the key to a good TT system, for both lowering Ra values and just as important for ensuring the TT systems stability...

I think others have brought up the other incorrect factors of your OP and by the sound of it, you seem to be in the process addressing them...
 

Reply to Hot Tub in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
334
  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top