The hottub is 8.1kw so will be 35A max output , I’m going to put it on 6mm 3core swa to an isolator then to the hottub. Would a 40a b type be sufficient for this ? Or would it be better to put it on a 40a c type mcb? Thanks
 
I’ve heard of some hot tubs having a spike when starting up and people thatve put them on a type c aswell as b just wanted to confirm what would be better
Does the manufacturer specify a particular protective device and will ADS be met with type c?

I'm asking questions as your profile indicates trainee status and OP provides insufficient information to provide an empirical answer.
 
While the 'hot' bit of a hot-tub load is resistive, there can be fairly beefy pumps for water jets and bubble jets, so I can understand there being a significant transient in load current if pumps are turned on while the heating element is running!
Edit: But as above, that doesn't mean bodging protection to avoid a problem!
 
Does the manufacturer specify a particular protective device and will ADS be met with type c?

I'm asking questions as your profile indicates trainee status and OP provides insufficient information to provide an empirical answer.
It is quite an old tub so doesn’t have the manufacturer instructions and cannot find out what it is, the only thing I could find on it is the max output that was 8.1ka
 

Reply to Hottub mcb selection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
I have changed the supply to a 16 amp mcb , my ZS at the bin store light is 1.29 ohms ,fault current of 186 amps. my read of the time current...
Replies
7
Views
834
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
757

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top