My house is undergoing a few modifications and I have some questions on the work required. I’ve read various books, etc on the 17th Ed regs, but I’d be grateful of getting some clarifications or comments on the following:
The existing cables under the ground floor are run loose between the joists and lying on the concrete floor. Is this OK or should they be clipped, run in trunking, etc? Correcting this would require a lot of extra work!
I have determined that a 10mm2 earth bonding wire is required for the water and gas supplies and this is run back to the CSU. Nothing installed at the moment. This seems straightforward. However my understanding is that equipotential bonding in bathrooms, etc should not have an earth cable back to the consumer unit, but should instead be connected to the earth in the circuit nearby. Is this correct? Some of the existing equipontential bonding in the house does have its own connection directly back to the CSU, which I don’t think is correct.
I have a split load consumer unit: a 60A RCCB protecting ring mains and cooker with MCBs and the lights, alarm, central heating off the unprotected side with MCBs only.
I am also having a new bathroom installed. There is space to run the lighting, fan, shaver point, etc from a new circuit on the RCCB side of the consumer unit. I assume that there should be no issues with this, other than zoning requirements, etc.
I want a new radial circuit to feed only a double socket for the fridge/freezer, but without RCD protection. The cable will be run under the floor and up inside a stud wall. Taking into account safe zones and running 50mm below the surface I also understand that the cable will require mechanical protection (no RCD). In this case SWA cable would be an easy option. The run is only about 10m long.
The existing cables under the ground floor are run loose between the joists and lying on the concrete floor. Is this OK or should they be clipped, run in trunking, etc? Correcting this would require a lot of extra work!
I have determined that a 10mm2 earth bonding wire is required for the water and gas supplies and this is run back to the CSU. Nothing installed at the moment. This seems straightforward. However my understanding is that equipotential bonding in bathrooms, etc should not have an earth cable back to the consumer unit, but should instead be connected to the earth in the circuit nearby. Is this correct? Some of the existing equipontential bonding in the house does have its own connection directly back to the CSU, which I don’t think is correct.
I have a split load consumer unit: a 60A RCCB protecting ring mains and cooker with MCBs and the lights, alarm, central heating off the unprotected side with MCBs only.
I am also having a new bathroom installed. There is space to run the lighting, fan, shaver point, etc from a new circuit on the RCCB side of the consumer unit. I assume that there should be no issues with this, other than zoning requirements, etc.
I want a new radial circuit to feed only a double socket for the fridge/freezer, but without RCD protection. The cable will be run under the floor and up inside a stud wall. Taking into account safe zones and running 50mm below the surface I also understand that the cable will require mechanical protection (no RCD). In this case SWA cable would be an easy option. The run is only about 10m long.