A plastic incoming service cannot, by definition, be an extraneous conductive part, ie. a part that is liable to introduce an earth potential or any other potential into an installation. Therefore main equipotential bonding is not required.
There is a standard test, described in GN8, to confirm whether an incoming service is or is not an extraneous conductive part. Using a high-reading ohm-meter, resistance is measured between the part and the MET of the installation. If above 56K Ohm it is not an extraneous conductive part.
Hi where do you get that value from? The figure of 22KΩ sticks in my mind but tbh i can't remember off hand where i saw that.