Hi!

Is there any way to know if I have a ring or a radial circuit in a division of the house?

Thanks!
 
In most cases if the supply breaker is 32A it is an RFC, and if 20A/16A a radial. But there can be exceptions to that by design, or by someone (typically builder or DIY) breaking an otherwise good design.

If you have a socket out (power off and tested to be off obviously!) with two sets of wires at the back of it and you isolate them there, then if measuring L-L or N-N you see a low resistance of under a few ohms then it is almost certainly an RFC.

Measuring CPC-CPC (earth - earth) should also form a loop, but in is not uncommon for the CPC of circuits to be linked elsewhere back to the main earth terminal, such as at a boiler, so that test is not as reliable as checking L-L and N-N.

If you find one of L-L & N-N is linked but not the other then you have a fault somewhere to be found and fixed!
 
Radial circuit has only one wire coming out of the CU from the MCB usually, a Ring circuit has two, but this does assume there are not two radials on one MCB.
That is the key word!
The breaker size sets expectations.
The number of wires set expectations.

But ultimately only testing confirms what is actually the case.
 

Reply to How do I know if I've got a ring circuit or a radial circuit? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
501
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
974
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

Well we called it a room, but it was only a hole in the ground covered with bit of canvas.
Replies
13
Views
760
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top