it's not always the tester at fault. sometimes you can get vastly differing readings on either side of an RCD. if in doubt, i take a reading from the L busbar. it should be close to the Ze value (allowing for parallel paths).
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss How do most of you prefer to do EFLI tests? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
it's not always the tester at fault. sometimes you can get vastly differing readings on either side of an RCD. if in doubt, i take a reading from the L busbar. it should be close to the Ze value (allowing for parallel paths).
Just tried that tel. 0.21 Ze on high current setting, 0.55 Ze on no-trip. 0.71 on no-trip at busbar....
Interesting....
So which answer would you say was the most accurate?
Hi Truckster,By measurement. I would check your original result by linking out the rcd, the no-trip test seems to give funny measurements sometimes.
Hi Truckster,
Can you just explain how to link out the RCD please.
Ive never used this method, but I too have sometimes experienced higher Zs results when using the no trip function on my megger 1553.
Thanks for your help,
Sav
Very trueHard to link out the RCD's with a Starbreaker unit....