gp66

enterd a house today to install 6 times firerated down lights in a bathroom.checked cu first customer said they had just recently had it upgraded by a british gas subcontractor split load rcd cu ,all well and good i thought .how wrong was i! climbed into loft unscrewd nearest j.b no earths to lighting circuit .no notice on cu to state niether up nor down lights had a cpc. asked customer to see test certs from cu instalation. and as he said it was put in two months ago by an niceic domestic installer.some how he had managed to get a r1 r2 reading on both circuits and a zs reading on both circuits. in comments on existing installation he had put NONE he also managed:eek::eek: to get a continuity reading on the water earth , very clever as there was no such earth,16 mm main earth put on test sheet >it was 10mm no buzzbar cover ,and when he had put the cover on the cu he had screwed through the top insulation on the 25mm main incoming line.god help us !!!
 
Well if it was a PIR then code 4 if all items are class 2 and the DB has a notice to indicate lack of CPC's to the lighting circuit etc etc.
Code 1 if class 1 fittings are installed.

If it's an EIC following a board change then you simply can't connect the circuit while class 1 items are in use.
If there are only class 2 items and the notice mentioned above is present then you record this situation in the departures and comments box on the EIC.

The best action is of course to persuade the client to have at least the offending lighting circuit rewired.
 
good clarification, IQ. i would only ( reluctantly)connect such a circuit as a temp measure so client would have lighting untill rectified.
 
Last edited:

Reply to how do they get away with it ?????? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
207
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
902
davesparks
D
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top