How do you test RCBO's Same as RCD's | on ElectriciansForums
Discuss How do you test RCBO's Same as RCD's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Bul
May be a silly question but are rcbo's tested the same way as RCD's?
If you read the manufacturers leaflet that comes with them some require you to remove the earth fly lead prior to testing. i do it as a matter of course and have not actually checked to see if it affects results. I know with some it can affect loop impedance tests.
Have seen many a CU with them cut off mind!
The 'function earth lead', does just that I believe. Cut it orrffh or not connect it might cause some functional problems. The earth & neutral fly leads have to be disconnected, if the manufactures state this, during IR testing, as far as I'm aware?
Obviously,MI should be adhered to,if you are writing down the test and result,but you could not damage any RCBO,using standard,IR test gear.
On the schedule of test results simply put 6100* instead of 60898/3036/etc etc. Obviously the x1 x5 results are on the far right hand side..
*Bit drunk and can't recall whether it's 009 or 008!
Reply to How do you test RCBO's Same as RCD's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
davesparks
Agreed. I wasn’t actually intending to suggest there is any issue with what you suggest, it would work and all devices would work to the best of...