On the schedule of test results simply put 6100* instead of 60898/3036/etc etc. Obviously the x1 x5 results are on the far right hand side..

*Bit drunk and can't recall whether it's 009 or 008![/QUOTE


BS EN61009 RCBO
BS EN61008 RCD
 
You need to test the RCBO's before connecting the circuit ... Then take the Zs at the end of the circuit. Obviously you can't do global ir tests so ir tests on the circuit come before the Zs
 
You need to test the RCBO's before connecting the circuit ... Then take the Zs at the end of the circuit. Obviously you can't do global ir tests so ir tests on the circuit come before the Zs
Thank you so much for your help. Appreciated.
 
you treat the rcbo has a mcb but having a mcb you will have the tails going to the neutral bar from the circuit and the earth goes to earth and the line into the mcb.. on a rcbo the line and neutral goes in to the rcbo on the rcbo the fly lead neutral goes to the neutral bar & the fly lead earth white goes to the earthing bar with the earth from that circuit .
[ElectriciansForums.net] How do you test RCBO's Same as RCD's
 
Last edited:
Many thanks, I've just never thought about it. Should test sheets then say RCD / RCBO tests?
Only if you ignore the definition of an RCD.

What you are referring to as an "RCD" is in fact an RCCB. It is just one of many types of RCD, which includes RCCBs; RCBOs; SRCDs; PRCDs etc.
 
Thanks for all your comments. I can see how obviously silly my question was. I respect the forum members opinion's and appreciate all advice.
 

Reply to How do you test RCBO's Same as RCD's in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
486
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
956
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
607
  • Question
It is not that they don't trip, it is that putting a probe in the front of the RCBO to contact the terminal bypasses the sense coil so the RCBO...
Replies
7
Views
771
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top