How is a generator earthed and given neutral? | Page 2 | on ElectriciansForums

Discuss How is a generator earthed and given neutral? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 3, 2015
Messages
348
Reaction score
35
Location
London
Hi

I have a question i cant seem to get an answer too.

If you have a portable generator and you plug for instance a fridge or any appliance directly into it, how is the neutral/earthing provided??

I know already that normally you can connect the neutral and earth from an existing installation

But what if you are for example somwhere random and i plug a fridge into a generator where is the neutral coming from? Surely it cannot be from the casing as if someone was to lift the generator up they would get a belt from the supposed to be neutral return path?

Thanks in advance
 
QUOTE - [how is the neutral/earthing provided??].
how is the neutral provided
or
how is the earth provided
please elaborate ?
There’s a number of ways to do this.
The manufacturer’s can link from one end of the coil to the casing of the generator. That end becomes neutral.
The manufacturer’s can link between the Earth and Neutral terminal at the socket (would need a conductor taken from the Earth terminal to generator chassis).
The user can make up a short plug and lead linking the Earth and Neutral at the plug and with an RCD and Earth rod at the other end.
 
When normal electric is generated you have a star point and that is grounded thus u get your neutral off that point you dont just get a neitral from anywhere its earthed???

The first thing you need to appreciate properly is the difference between Neutral (N) and Earth (E)

Earth is the conductor that provides a low-impedance path to the Earth (i.e. the body of the planet) to prevent hazardous voltages from appearing on anything you might touch... It's the 'fault condition' return path if you like.

Neutral is the circuit conductor that normally carries current back to the source. - The normal return path.

So, for example, in a normal household setup we (hopefully) have a device that monitors the 'balance between live and neutral currents on a 'what goes in must come out' basis; any imbalance means that current is returning to its source via the protective earth (rather than neutral) - which means something's gone wrong! - And in these circumstances we want to quickly isolate both live and neutral paths.

You will, I hope, appreciate the need for RCDs - ELCBs GFi's however you fancy calling them? And have an idea that's (roughly) what they do? - And hopefully the penny will begin to drop that beyond the RCD, neutral and earth are two different things; even though they might be physically linked elsewhere in the greater scheme of things?

So far so good?

Now... 'When you generate electric' you might or might not have three 'generator coils' in the machine. So, let's think of a single coil generator for now rather than confuse things thinking about three-phase...

Thinking about the solitary output winding...

As the machine (generator) goes through it's cycle one 'leg' of the coil 'pushes' current while the other end 'puls' it back it, and vice versa as the thing goes round. Thus; neither leg can be said to be inherently either live or neutral - In fact, what's delivered to homes on the U.S. system is almost-precisely that... They actually get two 'hot' wires fed to the house which measure 240v across these connections called L1 and L2. Not everything in the US runs on 120V! (Not to get too bogged down - I'll gloss over the vagueries of the American system, it's centre-tapped neutral etc and how the 120v is derived etc...)

Let's get back to the simple single-coil generator... as others have suggested, neither L1 nor L2 are 'inherently' neutral conductors they are opposite ends of the same phase.

Following me so far?

Let's go back to your picture of "When normal electric is generated" or more accurately when 'normal' electricity is dropped via the distribution transformer down to 240V (or so) to be fed as a single live wire to your home...

The three SECONDARIES of the transformer (up a stick in a field or hidden away somewhere in a small building) are indeed each connected at one end to a common star point... Which is then neutral relative to the three phases. - As we only want only one phase to our house, to get power to us we need to be 'sent' the neutral and the phase.

Now... Hopefully it's becoming clearer that in this situation there is no inherent reason for there to be a relationship between neutral and earth. One useful way to think of this (although its strictly-speaking incorrect) is that the live wire is the 'send' and the neutral is the 'return'.

There are a few practical and safety issues with that though.

Because there is no relationship between Neutral and Earth it's possible for there to be a significant potential difference between them! ...Which, should you become the conductor in the earth-neutral path can be really quite distressing.

In normal distribution, it's both convenient and safer to tie neutral to earth at the transformer (power station if you like).

Because, by this means, you've forced a relationship between neutral and earth it therefore becomes possible (and common) to 'send' a combined Protective Earth/Neutral (PEN) conductor to 'partner' the live. - The neutral for the system being derived from that.

Now... Let me get back to your original questions...

If you have a portable generator and you plug for instance a fridge or any appliance directly into it, how is the neutral/earthing provided??

Well... Earth is the Earth itself; literally Terra-firma. You could connect to the earth of an existing system or connect the frame of the generator to a buried rod. If you don't, the generator - and potentially the appliance - is not earthed.

- And it's because the manufacturers cannot be sure that their generators will be earthed that they leave the as output 'floating' - effectively L1 L2 (like wot the Yanks use) or the 'push-me-pull-you' ends of the single phase.

If you just connected (for example) L2 (as 'nominal' neutral) to the frame/earth pole of the generator and fail to tie it to an effective earth you can create a situation where the frame is sitting at a high enough voltage relative to earth to present a shock hazard! - Not only the frame of the generator but any appliance with an 'earth' connector!

This is a significant hazard in the film, TV and entertainment industries where generators for high-powered lighting and signal equipment are common. - One thing I'd strongly advise against is making up ANYTHING that links Neutral/Earth at the generator output! - This could only ever be safe if the operators fully understood the issues and you could be guaranteed that the generator would only ever be used connected to a proper earth.
 
......- This could only ever be safe if the operators fully understood the issues and you could be guaranteed that the generator would only ever be used connected to a proper earth.

Can you repeat that?

If you don't understand most of the above
! --LEAVE it ALONE-- !

Theme to ( Float - ON ..... ) ..plays gently in background
 
It's unfortunate that you can only muster such an infantile response... It would be more adult, if you disagree, to explain why. That way a consensus might be reached.

Yes, my explanation was long-winded. but as a former college lecturer I could see that the O/P just wasn't taking onboard the 'odd' fragments bourne on assumed knowledge that were being thrown. - and it's the O/P's questions I was attempting to answer.

Sometimes - even with someone who is at 'improver' level - you have to go back to basics and frame them in the simplest terms properly - that's one of the basics of andragogy.

As to my closing point...

It would appear the O/P hasn't-quite understood something basic; indeed, many lurkers on this forum will be members of the general public arriving here having searched for information on a particular thing - providing them with just enough knowledge to be dangerous isn't wise.

Simply making up some random device that shorts one end of a generator winding to the frame of the generator is dangerous. -Arguably almost as dangerous as the lengths of flex you'd sometimes find lying around with a 13A plug at each end made for the purposes of 'backfeeding' - but I digress.

Despite some of the nonsense I've seen in articles written and published by people and organisations who ought to know better, the notion of a 'floating earth' is really rather vacuous; rather like being only slightly dead! - The practice doesn't create any kind of earth at all, what it does - all it does - is create separate paths for normal and fault return - which assuming an RCD is included the charade might be an attempt to get the thing to function - but it's simply making exposed conductors part of the fault return path.

I personally know of a couple of incidences - thankfully many years ago - where cameramen, setting up lights powered on this principle have got belts when they came into contact with the stands of lamps powered from different sources.

On (most - you still come across a few run by eijits) film sets these so-called 'floating earth' sets are BANNED for anything but solitary class II appliances used for less than a day, and have to be run in a stewarded area. - Most sets have stern warnings on them about earthing them properly.

Even if this contraption includes an earth 'spike' and is intended to be used driven into the ground with the fault-return being a proper earth - which is, to be fair, what was suggested - unless you can be absolutely sure the end-user understands this fully, the device is dangerous to have around.

One of my neighbours, for instance, is a keen caravanner... In use he kept his 'proper earthing'/RCD contraption (sold to him by the caravan shop) in a sports bag under the van to keep it dry! - He was subsequently curious about the 'slight tingle' he got when he touched certain metal parts of the van while standing outside on wet grass in bare feet. - I say he's lucky as he is both elderly and has heart trouble. And I told him to go buy a mallet!

...Float on indeed, float on up on gossamer wings if you like! And do give St Peter my regards when you're chatting; tel him I won't be 'round for quite some time!
 

Reply to How is a generator earthed and given neutral? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K
  • Question
Thank you so much I have spent hours and hours looking for this answer, appreciate your time and comprehensive reply. I will look further into the...
Replies
2
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top