Last year we rewired a bungalow on a large private estate which caters for mentally ill patients. It had 5 bedrooms each with it's own wet room. The builder wanted a 10kw shower in each wet room but as the incoming sub - main was only 16swa protected by a 60amp fuse we told him no. We ended up with one electric shower and 4 mixers off the combi. The client needed a back up in case of boiler breakdown.
There are six identical bungalows and now the next one is ready for refurbing. The builders had two other contractors in to price the rewires. One's told him that 3 x 10kw showers will be ok and this has made the builder happy.
I've spoken to staff in the original bungalow who inform me that the normal morning routine is for two showers to be used at the same time usually while breakfast is being prepared (with electric oven and hob)
I'm sticking to one shower so it looks like I'll not be getting this one.