Hello,

Question number 2.

I didn't get shot down in flames with the first question so I feel able to ask another.

How many cables can you have in each MCB in the consumer unit and more importantly why?

This is not in order to try anything myself but I do want to try and have some basic knowledge before I start the domestic installers course.

Thanks..
 
The correct answer is as many as can safely be fitted and clamped securely as long as the mcb rating dosn't overate any of the cables incl' calcs, so you can have 3 x 1mm cables from a 6 amp lighting breaker as long as the loading etc have all been taken into account, its not bad practice nor does it contravene any reg's...

I was taught at College that a MCB can be used as an outlet for a spur, so going on that a RFC can have one unfused spur per outlet, the answer has got to be three...
 
i wouldnt put any emergency stuff like fire alarms onto any other breakers , if there is a fault in the circuit its shared with it will trip out and the fire alrms will lose power and go inot power saver mode, thats when you kind of over step the mark

Not 'fire alarm systems' but mains smoke detectors are better connected to a regularly used lighting circuit, reason being that the occupants will notice any loss of lighting far sooner.

On the original MCB issue, as long as the connections are mechanically and electrically sound, there is and never has been a 'limit' on cores terminated at a device.
 
I was taught at College that a MCB can be used as an outlet for a spur, so going on that a RFC can have one unfused spur per outlet, the answer has got to be three...

My example is lighting circuit and as such is numerous radials from mcb, your relating to a ring main only in a 32amp mcb where its permissible to also fit a third wire in for a spur as well as the ring, as i mentioned before as long as the design load of all the cables in total dosnt exceed the mcb rating and the circuits are individually sounds and installed and calculated correctly then the only thing limiting you is having good sound termination of all conductors associated, and exception to this rule as i believe you've confused the issue is a ring main - where the mcb exceeds the rating of a cable (2.5) that maybe spured but this set-up is in most cases safe as the spur is usually load limited by a plug fuse or spur etc
 
I like this thread, a very simple question with potentially complex answers.

In the UK does an MCB fulfill the legal requirement of circuit isolation even though it's a single pole device?
If it does, do the UK regs require that all circuits can be individually isolated by means of the MCB?
 
Thanks all. Again I didn't expect such a good response.. I'm beginning to like this site!

I thought the answer would be a lot more complicated than just a certain amount of cables, so thanks for all the explanantions. I may actually pass!!
 
I was on a job just after qualifying back in 2005 and came across a 6A mcb with 4x1.5mm cables in. I phoned my part p scheme provider for advice to see if this situation was acceptable. I was told it is acceptable if loading etc was taken into account but is not best practice. I personnally wouldn't do it but can see the reasons for. As its my name on the certificate its me that's got to answer for my work!
 
Not 'fire alarm systems' but mains smoke detectors are better connected to a regularly used lighting circuit, reason being that the occupants will notice any loss of lighting far sooner.

On the original MCB issue, as long as the connections are mechanically and electrically sound, there is and never has been a 'limit' on cores terminated at a device.
Totaly agree with iq . it states something like this in the OSG.
 

Reply to How many cables can you have in each MCB in the consumer unit? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top