Hello all, just wondering in an office with lots of it equipment how many computers would you put to one 30ma circuit?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss How many computers to 1 30ma rcd in the UK Electrical Forum area at ElectriciansForums.net
???say again??Thanks all, guess I'll leave off rcd or try rcbos
You're going to need an inhaler at this rate if you're not careful Mike!???say again??
Rcbo is an rcd just with built in overload protection so basically an mcb and an rcd rolled into one so it will be rated at a certain mA as well.
Maybe he means a few on each RCBO rather than the lot protected by a single RCD.
If they are insistent on rcd protection then fit rcd sockets rather than an rcd or rcbo at the db. The earth leakage from 4,5,6 computers depending on efficiency and age can trip them very easily