I used to do classrooms and I fitted RCBO's from the Schneider SI range which filter and ignore the designed leakage and only trips under normal fault earth leakage conditions. This allows more computers than a standard Earth leakage device and reduces the number of circuits required.

As you are limited anyway to the computers on your circuit - does it really make sense to wire rings, would not radials be a cheaper solution here.
 
I used to do classrooms and I fitted RCBO's from the Schneider SI range which filter and ignore the designed leakage and only trips under normal fault earth leakage conditions. This allows more computers than a standard Earth leakage device and reduces the number of circuits required.

As you are limited anyway to the computers on your circuit - does it really make sense to wire rings, would not radials be a cheaper solution here.

Trouble with a radial high integrity circuit you need to use a duplicate cpc bit difficult if you use Tin with cpc, not a problem with a RFC
 
Rings or radials are irrelevent, the fact is the op is planning on 14 PCs connecting to 7 twin socket outlets, it is a mistake and he won't listen, we all know what is needed, we know what to suggest but he won't listen, so god help his customer, simple maths but still no joy in persuading him, lots of help but no cigar at the end of it, I give up.
 
Trouble with a radial high integrity circuit you need to use a duplicate cpc bit difficult if you use Tin with cpc, not a problem with a RFC

Yes but only issue if not contained then its a 4mm earth to last socket for the return but if in trunking etc its a doddle... I don't see this as a problem IMHO, although certain set-up won't be as suitable as others agreed.
 
Don't add 14 PCs to one circuit with one RCBO on it
 

Attachments

  • [ElectriciansForums.net] How many computers to 1 30ma rcd
    imagesAOUG83K2.jpg
    11.5 KB · Views: 63
I was involved with one installation in a school, installation and testing only mind you.

We put ( I think) 8 PCs on each ring with the earthing split across each terminal (i.e. not doubled up)

I always understood to allow for up to 10mA earth leakage per PC.

Just my two penneth for what it's (NOT) worth!
 
Rings or radials are irrelevent, the fact is the op is planning on 14 PCs connecting to 7 twin socket outlets, it is a mistake and he won't listen, we all know what is needed, we know what to suggest but he won't listen, so god help his customer, simple maths but still no joy in persuading him, lots of help but no cigar at the end of it, I give up.

Suppose you can lead a horse to water but you can't make him drink it, think you are right :leaving::leaving::leaving::leaving:
 
I was involved with one installation in a school, installation and testing only mind you.

We put ( I think) 8 PCs on each ring with the earthing split across each terminal (i.e. not doubled up)

I always understood to allow for up to 10mA earth leakage per PC.



Just my two penneth for what it's (NOT) worth!
10mA per PC so as most rcd's trip between 18 and 30 mA then you can only plug 2 pc's in ?
 
I was involved with one installation in a school, installation and testing only mind you.

We put ( I think) 8 PCs on each ring with the earthing split across each terminal (i.e. not doubled up)

I always understood to allow for up to 10mA earth leakage per PC.

Just my two penneth for what it's (NOT) worth!


what kind of cheap Chinese tat do you work with "voltselectrical" that leaks 10ma to earth?

3.5ma is the max allowed i believe on uk ict equipment in the home (bassically pc's)

considering bronze certifed psu are 80% efficent and platinum 90% i doubt they will leak much to earth

they recommend 6/7 here

https://www.google.com/url?sa=t&sou...BszM8QYDw35DllZlA&sig2=Gv97a5TyT7XqpzHbblfSLw
 
Last edited:
what kind of cheap Chinese tat do you work with that leaks 10ma to earth?

3.5mah is the max allowed i believe on uk ict equipment in the home (bassically pc's)

considering bronze certifed psu are 80% efficent and platinum 90% i doubt they will leak much to earth

I was quoting post 40 .... seriously shank you should know im not that out of touch! :dunce2:

The question mark at the end of my post is a clue to my approach on this response.
 

Reply to How many computers to 1 30ma rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

  • Question
Leaves the potential nuisance of knocking off a raft of equipment unnecessarily
Replies
7
Views
1K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top