How to carry out RCD test for shower? | on ElectriciansForums

Discuss How to carry out RCD test for shower? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

N

nazoom

Hi

My exam is coming soon and I have a question.
My installation is single phase , TN-S. There is a shower unit protected by the RCD. My questions are:
Do I carry out RCD test at the RCD itself in the C/U or do it at the shower unit itself? If at the shower unit where does the tests leads go?

Many Thanks.
 
Ah, ok. You can carry out the test at the CU. Line lead to 'line out' on RCD (bottom left), neutral lead to 'neutral out' on RCD (bottom right) and earth lead to earth bar.

Edit: Presuming that it's a normal RCD :D
 
To complete the picture you're testing the RCD only with this test (that's why it's with loads disconnected, so you can be sure that only the trip current from the meter is being used to trigger the RCD). The Zs (in combination with the other tests) of all the other circuits being within spec is sufficient proof that the RCD will work for the circuits routed through it.
 
ok, but why then is the RCD trip results on an EIC on every circuit, why not just have one box for the entire cert, or 2 boxes x1 & x5
 
ok, but why then is the RCD trip results on an EIC on every circuit, why not just have one box for the entire cert, or 2 boxes x1 & x5
A good question, I'll pass on that one, that's a question for the form designer.

For an RCD (as opposed to RCBO) I use two separate lines on the form and record the times for x1 x5 at both 0 and 180 for posterity (one line for 0deg and one for 180deg).

If you did test the RCD from each circuit, you would actually get slightly different timings for each point/circuit tested (because of the EFLI from that point on the circuit being different for a radial for example).

The maximum Zs values have been worked out to ensure that sufficient fault current can flow to cause the device to trip. You can see the advantage, it's easier to do at the CU; you need to reset the RCD for each test (5 tests, 4 trips, 5 resets). The more modern tests have an auto mode making it even easier. Imagine the situation if you were trying to test the upstairs lighting circuit. You'd be up and down stairs a lot if working alone on it.

It will be the same if you are ever asked to "ramp test" an RCD or RCBO, you do it at the device. HTH.
 

Reply to How to carry out RCD test for shower? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
Used loads of them, but usually the Hager units. (Although these aren't in a steel enclosure as they are not designed for the UK market.) Any of...
Replies
3
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top