Guest55
As for recording 0 & 180 figures i only write down the highest / worst of the 2.
Can get a bit cluttered otherwise lol.
Can get a bit cluttered otherwise lol.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss How to carry out RCD test for shower? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yep, that's all that's required (and I don't do that for RCBO's, only for RCD's covering more than one circuit).As for recording 0 & 180 figures i only write down the highest / worst of the 2.
Can get a bit cluttered otherwise lol.
As for recording 0 & 180 figures i only write down the highest / worst of the 2.
Can get a bit cluttered otherwise lol.
Some old rcd testers don't even test 180 degree trip times
Hi,
Ok I can see the logic in testing the RCD at the board and agree with you all, but why is it then when assesors come to inspect us and they want an RCD test for kitchen sockets say for example, we use the plug in lead from the MFT ? Why not just test at the RCD itself? Would the assesor say anything to that, I mean having an exposed CU and working live ( safe isolation, not working at a live board etc ).
Sorry if thats a thick question everyone !!
Best regards,
Sav
I know, in fact it might just be me but I reckon they usually fail more often on 180!Amazing really when you consider how different the results usually are.
I agree with Sav. The main reason why I asked about where do we carry out the RCD test because I was told by one of my supervisor that I should carry out at the light (ceiling rose) However another supervisor told me that I can do it at the RCD itself!! So I got confused!! Which is right?
Thanks