Record the Highest ZS you get from the circuit, IGNORE the 5amp FCU that only protects the cable and not used for disconnection times just over load on the cable
Refer to the 32A MCB that is in the CU for Disconnection times which i believe is 1.15 ohms unless its protected by a RCD then it can be up to 1667 ohms.
so your 1.27 ohms is WELL within limits for disconnection by a RCD
TNS system should be 16mm earth to the CU and the bonding in 10mm
Refer to the 32A MCB that is in the CU for Disconnection times which i believe is 1.15 ohms unless its protected by a RCD then it can be up to 1667 ohms.
so your 1.27 ohms is WELL within limits for disconnection by a RCD
TNS system should be 16mm earth to the CU and the bonding in 10mm