Record the Highest ZS you get from the circuit, IGNORE the 5amp FCU that only protects the cable and not used for disconnection times just over load on the cable

Refer to the 32A MCB that is in the CU for Disconnection times which i believe is 1.15 ohms unless its protected by a RCD then it can be up to 1667 ohms.

so your 1.27 ohms is WELL within limits for disconnection by a RCD

TNS system should be 16mm earth to the CU and the bonding in 10mm
 
thanks steve, thats a great help to me. I did not realise the rcd increased the value up to 1667, thought that was just for TT system. Im learning a lot from you guy's so thanks again for all your help.
 
one last question, lf using a wander lead connected to the earthing terminal firstly and then the line conductor(at the consumer unit) and measuring from those points to the line and cpc at the furthest lighting point and the corresponding terminals. will ,when added together with ze will equal zs?
zs=ze(R1+R2) would this be one way to calulate zs for the lighting circuit?
 
Last edited by a moderator:
That is a novel way to get your R1+R2 using a wander lead, normally you only use the wander lead for R2. To save you trailing a lead around just link the LINE/CPC at the CU and then take your readings at the points to get R1+R2.

Yes quite right by getting your R1+R2 and then adding the Ze will give you your Zs. This is often the way it's done on initial verifications. For a PIR I have to admit I would do a live test espicially in a commercial/industrial enviroment. I do realise that by doing it live you can introduce parallel paths, but IMO that is not a bad thing really, as that will be the status of the installation if a fault occurs.

Now with RCD protection so prevelant and "soft" test being done to avoid tripping, you can produce very high results on a Zs. Though the flip side to this is becasue of the use of RCDs as additional protection the Zs reading is becoming less and less critical as 1667 is your important figure and if you can't achieve below this then you have serious problems.
 
thanks malcom. For this installation which has a lighting circuit connected through a fused spur,should i do the figure of 8 for the ring and then test the furthest lighting point with line/cpc crossed connected at the furthest lighting point and that will give me R1+R2?
, thanks again .
 
Last edited by a moderator:

Reply to How to certify a ring main with lighting circuit taken of a fused spur??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
155
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
522
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
465

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
706
If it's going to be an emergency stop and not just a stop, then other factors come into play depending on what sort of machines the emergency stop...
Replies
11
Views
973

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top