I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor.
Motor's stator windings are connected in delta.
I've read in some textbooks it is necessary to open motor's junction box and disconnect terminals and remove jumper bars (which are used to establish delta or star connection) and only then perform insulation test between:
a) each winding and earth and
b) each of the windings.
I think this might not be necessary and that it is enough to test the insulation from the motor's contactor output between any of the phases and earth.
This will let us know if there is an insulation problem between windings and earth.
However, testing this way doesn't allow us to measure the insulation resistance between each of the windings.
Questions:
1. How likely is it that there is a low insulation reading between windings and that this reading will not manifest itself when performing insulation test on the motor's contactor output between any of the phases and earth?
2. I am using Megger MIT330 and testing 3-phase asynchronous squirrel cage motor which operates at 400VAC.
Which voltage should I apply when testing and for how long should the voltage be applied?
3. If I apply 1000V for 20s on motor's contactor output between any of the phases and earth, I notice an increase in resistance from 50MΩ up to 250MΩ during the first 20 seconds and then it remains steady around 250MΩ. Why does this happen?
4. What is the acceptable insulation resistance when testing resistance on motor's contactor output between any of the phases and earth for the 400VAC motor?
5. Why is this considered acceptable insulation resistance?
Motor's stator windings are connected in delta.
I've read in some textbooks it is necessary to open motor's junction box and disconnect terminals and remove jumper bars (which are used to establish delta or star connection) and only then perform insulation test between:
a) each winding and earth and
b) each of the windings.
I think this might not be necessary and that it is enough to test the insulation from the motor's contactor output between any of the phases and earth.
This will let us know if there is an insulation problem between windings and earth.
However, testing this way doesn't allow us to measure the insulation resistance between each of the windings.
Questions:
1. How likely is it that there is a low insulation reading between windings and that this reading will not manifest itself when performing insulation test on the motor's contactor output between any of the phases and earth?
2. I am using Megger MIT330 and testing 3-phase asynchronous squirrel cage motor which operates at 400VAC.
Which voltage should I apply when testing and for how long should the voltage be applied?
3. If I apply 1000V for 20s on motor's contactor output between any of the phases and earth, I notice an increase in resistance from 50MΩ up to 250MΩ during the first 20 seconds and then it remains steady around 250MΩ. Why does this happen?
4. What is the acceptable insulation resistance when testing resistance on motor's contactor output between any of the phases and earth for the 400VAC motor?
5. Why is this considered acceptable insulation resistance?