how to identify a pme system help | on ElectriciansForums

Discuss how to identify a pme system help in the Australia area at ElectriciansForums.net

L

lucus

hi all
i am just wondering how can i identify if a properly that used to be TT has been upgraded to TNCS (pme) one i recently done a job in used to be feed from a pole but now has been upgraded to underground concentric cable would you say this is pme?
 
so im looking for a different result on pefc and pscc there usually very simular in my experiance what am i looking for on the ze, a higher reading for live and earth compared to live and neutral as the earth is smaller than the neutral?
regards
 
On a PME system the PEFC and PSCC will be the same.

Your Ze reading should be lower tham 0.35ohms. If it is still a TT then the Ze wll be much higher than this and the fault currents will be different.
 
Thanks I know this is for a instalation with a main earth cable in place already I'm wondering if there's a test to see if there is pme available, as in when doing the ze I'm not just testing the neutral path, the supply company update the cut out but don't seem to put a new main earth cable.
 
Disconnect all bonding and test at 20ohm setting with line test lead on L and and neutral & earth leads together on the N in the CU.

If no PME you will get no reading.
 
Last edited by a moderator:
sorry but what am i testing here ze? also is this the no trip setting so it uses the neurtal? so im connecting both the neutral and earth leads together on the neutral of the cut out.
thanks allot lads just trying to get my head around this.
 
Last edited by a moderator:
Thanks I know this is for a instalation with a main earth cable in place already I'm wondering if there's a test to see if there is pme available, as in when doing the ze I'm not just testing the neutral path, the supply company update the cut out but don't seem to put a new main earth cable.

You cant do a test to see if pme is available if there is not an earth already connected.....you will have to contact the DNO for this info.
 
Disconnect all bonding and test at 20ohm setting with line test lead on L and and neutral & earth leads together on the N in the CU.

If no PME you will get no reading.

Surely for Ze test you're testing between the incoming phase terminal and the supply earth? Between Phase and Neutral would be for calculating PFC.
 
Cant understand the problem is there no earth visible? if its been upgraded by dno then an earth will be in place its there responsabilty so if theres not and your sure its been upgraded ring them and they can confirm for you.
You cant carry out a test to find out with no main earth in place between cut out and equipment.
 
Would this work to identify a pme? - Do a Ze test across L and E and then do a Ze across L and N. If the readings are identical then it is a tn-c-s. [not at all experienced on this sort of thing yet :eek:]
 
Would this work to identify a pme? - Do a Ze test across L and E and then do a Ze across L and N. If the readings are identical then it is a tn-c-s. [not at all experienced on this sort of thing yet :eek:]

Don't mean to be pedantic (do you believe me?) but a "Ze test across L and N" wouldn't be a Ze test.
 
sorry for the confusion what i am asking is if there is a way to test the neutral for a pme, what has happened is a house ive been doing work at used to be fed from a pole but has recently been upgraded to underground concentric but the supply company didnt fit any earth cable from the cut out and i am wondering if i can test to see if pme is available.
regards
 

Reply to how to identify a pme system help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top