D

Devon sparks

Hi new here :)

Can anyone suggest how I can improve my Zs readings on a TT system for my final cct's.

Already have split board with 2 x 30ma RCD's and type B breakers!

A Should I be changing to RCBO's?

B try adding more earth rods! dont fancy this as problematic...

C what can you suggest PLEASE..............................................................

The main Za reading is 181 ohms which is under 200ohms and I have had to install 3 eath earth rods to get this reading.

Many Tks Devon Sparks
 
usually your main bonding will bring the readings down. as long as all circuits are on RCDs, then enter 1667ohms on your schedule of test results. .... sorted.
 
Telectrix - Many Tks for your info......

Can you clear something up for me Looking a guide for Zs re circuit breakers and it says in the heading 0.1s to 5s and has reading - for a 32A Device on a type B mcb to BS EN 61009 @ 1.15

What's the best way to check the mcb will operate within said time???

Many Tks Again
 
if your Zs is above the max.e.g. 1.15 for a 32A type B , as you say, the MCB will not trip within the specified time. trherefore, you are relying on the RCDs to trip (for a TT ststem this is 200mSec.). the RCD is then acting as fault protection instead of the MCB. to comply with disconnection times then, the max. Zs is 1667ohms.
 
tt disconnection times for devices rated up to 32A 0.2 seconds and over 32A 1s your high readings are acceptable like tele said the max zs for rcd protected circuits (30ma) is 1667ohms which u think is 50v touch voltage divided by the 30ma
 
Hi,

Longer earth rods are better than more shorter ones and if you are using more than one rod these should be spaced apart by at least the length of the rods.

I personally would try to get the Ze as low as possible (easier said than done, I know!), but as the other posters have said max Zs = 1667 ohms for a 30mA RCD.
 
Hi Guys - Brilliant and Thanks very much for all your info :)
I will take on borad all you say,
N.B. Ground is very difficult as granite area, "real pain"....

So hopefully last question :

How can I best improve the mcb protection so I'm not relying on the RCDs to trip OR is it that is all that is needed for a TT ststem. I.E. the RCD TRIPS WITHIN 200mSec and the Zs is under 200ohms.

What should I put down on the test sht for Max Dis-con times permitted for each cct - 200ms???


Once again Thanks very much for the responce and Advice...

Great Forum well done
 
What should I put down on the test sht for Max Dis-con times permitted for each cct - 200ms???

​NO!! the 200ohms is the advised max. for the Ra of the rod. the figure you enter for Zs is 1667ohms.

and the disconnection times are 0.2sec for circuits up to 32A and 1 sec. for circuits above 32A

edit. makes note to read post correctly before replying
 
Last edited:
How can I best improve the mcb protection so I'm not relying on the RCDs to trip OR is it that is all that is needed for a TT ststem.

You have more or less answered your own question here, as Tel said above the RCD takes care of the disconnection times (for earth faults), unfortunately you have to rely solely on the RCD(s) for earth fault protection in this case due to the high Ze.
 
Last edited:
sorry, mate. mis read your last post as 200ohms, not mSec. you are correct, the 200mSec. is for circuits up to 32A.
 

Reply to How to improve Zs reading on a TT system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top