Good evening
I am currently a training to become an electrician. I do hold both initial verification and periodic testing qualifications however this is an issue I have never personally had to deal with and was never mentioned on any of my courses as often seems to be the case.
Basically I am wondering how you would hypothetically go about testing either a ring or radial circuit if you didn't have a seperate cpc but the conduit itself acted as this.
Look forward to hopefully getting a response and some clarity
Regards Harry
There are basically two reasons for SB, the special locations part is to do with reducing Ut to keep it below 50V, medical locations below 25V, back in the 16th agricultural locations required Ut below 25V as well I recall, but I don't recall now which specific amd, or if it ever changed in that entire edition.
The other part is to achieve disconnection times and was to reduce Zs by default, the regs are worded --- backward in a lot of cases.
I can’t even remember the 16th that well
Wish I had kept my yellow copy I used to pass the exam.
What I do remember from that time is the awful bonding and in particular the radiator clamps we used to supplementary bond the bathrooms
Looked hideous if you couldn’t hide them
No, I could get my 16th editions out, but as the disconnection times part are still in the current edition and GN8 for the 17th amd 3 there is not much point really, I will look up the regs spin posted up later, and see what actually changed.
So I have been in the loft and after looking for a red book realised I had a blue hard back copy.
[ElectriciansForums.net] How to test a circuits in steel conduit as the cpc
This is the latest version:
419.3 Except where Regulation 419.2 applies, if automatic disconnection cannot be achieved in the time required by Regulation 411.3.2.2, 411.3.2.3 or 411.3.2.4 as appropriate, supplementary protective equipotential bonding shall be provided in accordance with Regulation 415.2 and the voltage between simultaneously accessible exposed-conductive-parts and/or extraneous-conductive-parts shall not exceed 50 V AC or 120 V DC.
In the brown book 16th 413-02-15 is deleted in 1992 amd2
This reg is present in the green book amd1: 1992 16th though, and says pretty much the same as the blue book above (which I also have).
The 16th was a bit strange as there was at least one reset in between the green book amd 1 :1992, the blue book :2001 (no amd given even though it is almost a decade later) and the brown book :2004 both amd 1+2
Reply to How to test a circuits in steel conduit as the cpc in the UK Electrical Forum area at ElectriciansForums.net
My older card has it but my newer card doesn’t