Hi all I am having trouble trying to work out the total load and swa cable size.
I have 10 circuits in a outhouse 40 meters from the mains power supply 1 x lighting with 10 lights, 1 x lighting with 10 lights.
1 x 2.5mm radial for 2 heaters, 1 x 2.5mm radial for heater. 3 x 2.5mm socket rings with 3 sockets on each ring, 1 x water heater radial for 2 instantaneous hot water... I have calculated the lights at 100w per light x 20= 2kw, the heaters are around 3kw x3 =9kw.
Water heaters 3kw each=6kw... The problem is the sockets as I'm not sure what's going to be plugged in apart from a kettle. working them out at 13amp x 230v gives me nearly 3kw per socket x9 = 27kw which seems unrealistic... Adding all that up before diversity is 44kw which seems way ott for that. Thanks all
 
What is the reason you were given for converting to TT if its over a certain distance? And for that matter what value do you use for the distance at which you need to do this?
What do you mean by no extraneous parts therefore no need for PME?
None of this sounds 'old school' to me, more like nonsense!
Hi it was just the way was taught many moons ago regarding tt and outbuildings ,,, and the no extraneous parts was meant to indicate for this instance the out building is made of wood no metal, and if used tt would be no pme, but dnt worry about tt I going to use the tncs earth, sorry about the way I type not very good at typing on these small phones and new to forums cheers guys.. Also I will have update on what equipment is going to be used tomorrow so can make better assumption of ib of sockets,, sorry so late to reply had 12 hour day and at it again in 8
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham

Thread Information

Title
How to work out the total design load to find my swa cable size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
62
Unsolved
--

Advert

Thread statistics

Created
Ted Curly,
Last reply from
Ted Curly,
Replies
62
Views
7,779

Advert

TrueNAS JBOD Storage Server

Back
Top